Just run 2 - 14/3 nm cables and all those troubles go away. Now if they only made those darn jb's big enough to meet code life would be wonderful

That's what I thought but apparently you can't parallel the neutrals.

Try to keep up :grin:

I guess the only compliant solution is to feed the fan/light/heat/nitelite with power and run switch loops to the sw box.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
That's what I thought but apparently you can't parallel the neutrals.

Try to keep up :grin:

I guess the only compliant solution is to feed the fan/light/heat/nitelite with power and run switch loops to the sw box.


You don't parallel the neutrals. Each outlet in the fan/light/ heat/ nite light has it's own recep. with it's own neutral. Just split it up.
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
I guess the only compliant solution is to feed the fan/light/heat/nitelite with power and run switch loops to the sw box.
:D
It'll take a Porta-Push to squeeze the conductors into that fan jbox. 14/2 in, 14/5 to the switch box.
 

220/221

Senior Member
Location
AZ
Each outlet in the fan/light/ heat/ nite light has it's own recep. with it's own neutral. Just split it up.

Well then nevermind. The ones I have installed only had one neutral.
 

cowboyjwc

Moderator
Staff member
Location
Simi Valley, CA
1/2" FMC or smurf tube is sounding better all the time. :cool:

That's exactly what I was thinking.

I always thought that you paralleled conductors to make smaller ones into larger ones (two #12 instead of one #8 for 40 amps for example). In the case of the 14/3 and the 14/3 you are simply splicing the neutrals.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
The ex fan/light will not have separate neutrals but I don't see where it says they have to.
The NEC doesn't say it, but to have each neutral only supply the same loads as the hots in the same cable, and you have more than one cable, that's what would have to be done.
 

gndrod

Senior Member
Location
Ca and Wa
Installation #1
A bathroom will have a combination heat/vent/light appliance installed on a 120-volt/15-amp dedicated circuit.

Installation #2
A ceiling fan with light will be installed on a 120-volt/15amp lighting circuit. By NEC code can on 14/3 and one 14/2 Romex cable be used between the two double-gang boxes to provide the five conductors needed; or must five-single conductors be installed in conduit between the two double-gang boxes?

I am looking for serious responses and it is my hope that someone can help me understand these particular problems more clearly. Thank you for your help.

Questions: Installation #1...Your question has incomplete descriptive data. a) Please state size of bathroom sf area to determine lighting required. b) Please state type and size of heater such as resistant elements, or IR lamp. c) Please state if bathroom has 50% openable 3 sf window.

Answer: Installation #2...Yes 14-3 and 14-2 can providing the remote 2gg box is dead-ended. Loop is permitted by [404.2(A)] exception. Note: the white conductor insulation must be painted or taped black.
 

Flex

Senior Member
Location
poestenkill ny
Questions: Installation #1...Your question has incomplete descriptive data. a) Please state size of bathroom sf area to determine lighting required. b) Please state type and size of heater such as resistant elements, or IR lamp. c) Please state if bathroom has 50% openable 3 sf window.

why is that important?
 

gndrod

Senior Member
Location
Ca and Wa
Important...maybe

Important...maybe

My apologies Flex. I see you are commercial. A little explaining will help. Residential codes include other trades that impact the NEC in different ways. For instance, the IRC R303.3 requires artificial lighting and venting for bathrooms that do not have at least a 1.5 sf glazing opening for air circulation. In that case, the vent fan and illumination must be controlled on simultaneously. The sf of a bathroom requires 3w/sf [220.12] to determine the lighting sizing basically. (I.e. A bathroom 5' x 8' = 40sf x 3= 120 w lighting.) Does this help? rbj
 