I would run the hot and neutral to the appliance, and then the switch legs to the switch box.
I know that's not what the OP says, but thats what I would do.
I would agree. I think the answers to the OP's questions are "no" and "no" - neither NM installation as described would be NEC compliant due to having a cable that does not carry both the source and return currents associated with the circuit. I think that a compliant NM solution would be to use a 14-2 to the device to provide un-switched ungrounded and grounded conductors, and then use a 14-2 for each switch loop from the device to the switch (or closest switch, in the case of the 3-ways) and back to the device. In this case each cable carries the full source and return currents for the circuit (zero net current - a clamp on ammeter around any cable always reads zero).