Re: Restaurant POS...
If you need to have a non-GFCI receptacle or a UPS this close to a sink all of the computer receptacles and plugs should be LOCKING. This would exclude any loads that should be plugged into the GFCI. The locking receptacles should be labeled NOT GFCI.
 An electrical safety inspector I know is a bit critical of having to have every 15 amp and 20 receptacle in a commercial kitchen GFCI because it messes up computers. It also does nothing about 30 amp 120 volt appliances. Also, a lot of existing refrigerators have too much leakage current for GFCI to work. This amount of leakage aurrent is no different than how if you do not ground a 480 volt motor it will have a nasty tingle voltage even when brand new.
 If you are really worried about electric shock you also need to be doing continuous monitoring of the equipment ground like with 1,100 volt and 3,300 volt extension cords in mines. Mine cords also have shielding of the conductors as well so that the first fault is always a ground fault. There is GFCI protection for equipment that ignores normal current leakage to the shields and so forth. There is also impedance grounding of the power source so that ground faults do not burn clear so that the protective relays and the lectricians can locate the ground fault.
 The British have not had an electocution in their coal mines since 1964 so they must be doing something right.