Check out www.powervar.com. It looks like they are basically isolation transformers. (I'll be Square D wishes they could sell 360VA worth of transformer for $1700!!)
The voltages the tech measured were probably "high frequency noise" voltages. You can't measure that with a DMM.
Steve
Yes, the general rule is "One and only one" neutral to ground bond.If indeed there is a neutral-ground bond at the service disconnect, then should the neutral be separate, "floating", from the equipment ground in the panel?
Check out www.powervar.com. It looks like they are basically isolation transformers. (I'll be Square D wishes they could sell 360VA worth of transformer for $1700!!)
The voltages the tech measured were probably "high frequency noise" voltages. You can't measure that with a DMM.