A fellow inspector and I have been discussing this photo:
http://i739.photobucket.com/albums/xx37/augie47/HolidayInn021.jpg
(for this thread ignore bundling and strapping)
The romex you see is above a sheet rock ceiling. The sheet rock ceiling extends and becomes an acoustical tile suspended ceiling (these pictures were taken from being in (above) the lay in tile.
The romex is not directly above the suspended ceiling but is above the sheet rock ceiling so it would not seem to be a violation of 334.12(A)(2).
If the ceiling tile has a 15 min rating it seems it would comply with 334.10(3).
Would you consider this install a violation ?
http://i739.photobucket.com/albums/xx37/augie47/HolidayInn021.jpg
(for this thread ignore bundling and strapping)
The romex you see is above a sheet rock ceiling. The sheet rock ceiling extends and becomes an acoustical tile suspended ceiling (these pictures were taken from being in (above) the lay in tile.
The romex is not directly above the suspended ceiling but is above the sheet rock ceiling so it would not seem to be a violation of 334.12(A)(2).
If the ceiling tile has a 15 min rating it seems it would comply with 334.10(3).
Would you consider this install a violation ?