Romex laying on top of furring

Status
Not open for further replies.
Re: Romex laying on top of furring

Originally posted by electricmanscott:
That's also a good shot of a violation.
How so?

If we are talking national than maybe as the NM looks closer than 1.25" to the framing members it is parallel to.

If we talk MA than I do not see a violation as in MA the NM only has to be 3/4" from the strapping.

Take a good look at MA 334.17 about 1/2 way down the second paragraph.
 
Re: Romex laying on top of furring

Originally posted by Fred S.:
From a builder's standpoint those furring strips are not the ones the NEC refers to. The NEC is refering to furring strips intended to protect wires below an unfinished ceiling, or on top of a ceiling joist in an unfinished attic. As a practical standpoint j_e's method of support/fastening at joist points would meet the 1.25 requirement as long as they are only screwing the drywall at the joists and not all along the furring strips.
As Bob has already mentioned, the furring strips in op are used to support drywall. Most builders and carpenters refer to it also as "strapping".
 
Re: Romex laying on top of furring

Thanks everyone for some good replies. For the two who asked I am the inspector in the towns of Millville and Uxbridge and the assistant in Blackstone. j_Erickson I called the Milford office yesterday hoping to get an opinion from Mike but I missed him.

I contacted the person that did the work yesterday and told him that I consider the work a violation of NEC and MEC and to secure the romex as per 334.30. I also told him that I respect his right to appeal my decision and that I would not be offended if he did so.Thanks again romeo
 
Re: Romex laying on top of furring

Romeo, sounds like you have things under control there and you are a good inspector.

Bob, look closely at the picture. :D
 
Re: Romex laying on top of furring

Romeo,

I thought it was "you" posting, but I couldn't tell from the profile. I didn't know if someone was using "romeo" as a nickname. I didn't realize you were on the forum.

John
 
Re: Romex laying on top of furring

Yeah, Scott, what are you seeing that I'm not? From the picture, some nm's may be too close, but it's hard to say.
 
Re: Romex laying on top of furring

I have been away from the forum a few days, glad to see all is still the same here ;)


.30 is securing and supporting.
Romeo, I believe you are correct, as the cables in your scenario are properly supported, but not properly secured.

Bob's picture show the installation with the cables secured to the floor/ceiling joists. I see that as a compliant installation. 300.4(D) is for cables installed parallel to the framing member/furrinng strips.

[ January 07, 2006, 01:51 PM: Message edited by: pierre ]
 