can romex be used in a commercal building
can romex be used in a commercal building
334.10 Uses Permitted.
Type NM, Type NMC, and Type NMS cables shall be permitted to be used in the following:
(1) One- and two-family dwellings.
(2) Multifamily dwellings permitted to be of Types III, IV, and V construction except as prohibited in 334.12.
(3) Other structures permitted to be of Types III, IV, and V construction except as prohibited in 334.12. Cables shall be concealed within walls, floors, or ceilings that provide a thermal barrier of material that has at least a 15-minute finish rating as identified in listings of fire-rated assemblies.
FPN No. 1: Types of building construction and occupancy classifications are defined in NFPA 220-2006, Standard on Types of Building Construction, or the applicable building code, or both.
FPN No. 2: See Annex E for determination of building types [NFPA 220, Table 3-1].
(4) Cable trays in structures permitted to be Types III, IV, or V where the cables are identified for the use.
can romex be used in a commercal building
Not in civilized parts of the country :grin:
In commercial work here, line voltage requires pipe&wire, MC, flex etc. The exception here is low voltage (lights with a 12V remote transformer for example). In those cases NM is approved.
Welcome to the forum
That depends on type of building
even the 277V lights had Romex feeding them.
it was kind of fun when our tracer could not identify a circuit so we tried shorted the hot to ground and never could get the breaker to trip all we could hear was a loud hum and some vibration in the wall from the circuit shorting. I think I could have actually welded with this circuit with out tripping the breaker.
Close, not so much the type of building constructed but the kind of building that could have been constructed.
For instance you can run NM in a Type I or Type II building as long as the code would have allowed that same building to be Type III, IV or V.
Not in civilized parts of the country :grin:
In commercial work here, line voltage requires pipe&wire, MC, flex etc. The exception here is low voltage (lights with a 12V remote transformer for example). In those cases NM is approved.
Thankfully we used common sense in my part of the country, that is, until the NEC changed. There are literally thousands of commercial use buildings including supermarkets, high rise apartment buildings, office parks, etc wired with NM cable here in New England.
NM is rated 600 volts.
First off you where doing something incredibly stupid, that is a good way to get burned, shocked or maybe start a fire in a wall. I was a green Journeyman & still learning not that this is an excuse . Today I know better than to try to short out a circuit to find the breaker. my mind at the time was thinking this was no big deal because hopefully the Breaker would trip so we could ID the circuit. since the circuit tracer was not able to locate the circuit or I may have been using the tracer wrong.
it was the fact that they were zinsco breakers. Romex was located above suspend ceiling used as return air plenum.
Second off the fact that it was NM has absolutely noting to do with how long the breakers took to trip.
If I did something like this today I would need to have my Brain examined for doing such dumb move.
you are right to say I was doing something stupid.
Cameron
Sure but look at the result....:roll:
But the change that ended up prohibiting the use of NM above drop ceilings in commercial building was what the NM supporters gave up to get rid of the three story limit that was in previous codes.Thankfully we used common sense in my part of the country, that is, until the NEC changed. ...
But the change that ended up prohibiting the use of NM above drop ceilings in commercial building was what the NM supporters gave up to get rid of the three story limit that was in previous codes.