I visit forum often but haven't posted much at all. Today's failed rough-in inspection has prompted me to post tonight. I'm having a master bdrm addition built on to my existing home and had the rough-in wiring inspected today. Came home to a rejected sticker with the comment from inspector stating "14 wire not to be used in a 20amp circuit." I used 12/2 for my light and receptacle circuits with 14/3 for 3 way travelers and switch leg to fan light combo in bathroom. Being a former EC, I had quite a bit of nail on boxes and 12/2 wire laying around I could use so I did. I plan on using 15amp arc fault breakers for my brdrm circuits. Code book is at office but I'm pretty sure 15amp circuits in bdrm's are legal. Is the inspector assuming I will be using 20amp breakers based on the 12/2 I used? Can one not use 12/2 on 15amp circuit? Any thoughts?