running 480v machine on 380v

a0c3bb933f9005ff12d894a8ed7ed169.jpg

This was the feedback of miller tech assistant
 
a0c3bb933f9005ff12d894a8ed7ed169.jpg

This was the feedback of miller tech assistant
They probably mean, "We will not support this unit operating on 380 volts." But it very well might work. If you were my customer, I would find a transformer to use. But if this were my machine, I would hook it up and see what happens.
 
They probably mean, "We will not support this unit operating on 380 volts." But it very well might work. If you were my customer, I would find a transformer to use. But if this were my machine, I would hook it up and see what happens.
The original poster says that a transformer is not an option.
 
If you have a servicing dealer around you or the one it was purchased from, it might be worth a call to, to ask about having the CE filter added to the machine to make it compliant for your situation. Someone that works on the equipment, hands on, would likely be more knowledgeable on your situation. It's easy for a inexperienced desk support person to tell you NO, when they may not know themselves.

Clearly the portion of the manual that showed the CE filter for the Euro zone approved model, shows that it can be made compliant for CE use.
That servicing dealer would likely have access to a different factory support engineer that is more knowledgeable on the equipment, to give you a better answer as to what is required or why not, than just, no. Even if you obtained a transformer to use with it, that doesn't make it compliant for CE use.

getting a copy of the service manual with the schematics, may also shed some light on the differences between models.
 
Clearly the portion of the manual that showed the CE filter for the Euro zone approved model, shows that it can be made compliant for CE use.
No. This could simply be one manual for two different models.

I would trust the Miller tech support, I am sure they often deal with people buying welders that don't match their supply.
 
The original poster says that a transformer is not an option.
He may not find a transformer that is exactly the ratio of 380:460, but he just has to get in the range. He may even have to use multiple autotransformers to get close. But it CAN be done
 
He may not find a transformer that is exactly the ratio of 380:460, but he just has to get in the range. He may even have to use multiple autotransformers to get close. But it CAN be done
Have a look at the data:

5kH - 30kHz.

What do you make of that ??
 
Many thanks for everybody for the engagement.
Now I decided to use a generator by changing its excitation and control protection to work for 480v
Will this have any impact on the generator insulation withstand? Any concerns to consider for this transformation?


Sent from my iPhone using Tapatalk
 
Yes I know that. But it is a complex system and is not that simple as Emad has explained.
No it is not.

That equipment comes from the manufacturer in one of two input voltage, both rated for 50Hz. The item the OP has does not match the source voltage he has. The only way to make voltages compatible is with a transformer on the input, or the OP equipment needs to sold and the correct item purchased.
 
No it is not.

That equipment comes from the manufacturer in one of two input voltage, both rated for 50Hz. The item the OP has does not match the source voltage he has. The only way to make voltages compatible is with a transformer on the input, or the OP equipment needs to sold and the correct item purchased.
Um............................

"Hi Emad
This unit will not operate with 380VAC"

Seems pretty clear to me.
 
Last edited:
Yes I know that. But it is a complex system and is not that simple as Emad has explained.
This device is essentially a switch mode power supply. As long as you can get it to come on, the electronics inside will do whatever it takes to make the output. It is as simple as getting the input within a range that it will tolerate. If I couldn't get a new machine and I couldn't get a transformer that took me to the specs directly, I'd get whatever number of autotransformers as necessary to get close.
 
Um............................

"Hi Emad
This unit will not operate with 380VAC"

Seems pretty clear to me.
Which is why he needs a transformer to raise his supply voltage or he needs to by a different model. What is complicated about these two options?
 
Which is why he needs a transformer to raise his supply voltage or he needs to by a different model. What is complicated about these two options?
And that was the was the initial problem:

"A step up transformer with this ratio is not avaivlbe in the market"
 
Top