- Placerville, CA, USA
- Retired PV System Designer
In addition to less current per phase, if the load is balanced you only need to figure the voltage drop on the phase conductors, not the neutral.
Smart $...
And, if source is 3ph, 208Y/120 line-current is about 100A! Thus, line Ampacity is reduced from say 154Ax1.25~190A, to ~130A, for unity-PF loads!
Phil
I think he is saying if it is three phase vs single phase and you balance the loads across the phases you have less current per phase conductor.
I still think 551.40 does not allow use of a 208/120 volt system. It says a system rated 120 volts - two wire, or a system rated 120/240 - three wire. The place it says 208(-230) is where it is referring to rating of connected equipment, not the supply system. Can't say I know why they don't want a 208/120 supply but I think that is the intention.
Have better thinking cap on today...In addition to less current per phase, if the load is balanced you only need to figure the voltage drop on the phase conductors, not the neutral.
Why is 551.40 worded the way it is if they didn't intend to prohibit 208/120 volt systems? Again I don't know any great reason to prohibit a 208 volt system in the first place but they kind of excluded them the way they worded things IMO.Have better thinking cap on today...
Distribution at the pedestal feeder level can be 3?.
208Y/120V 3? 4W is definitely permitted at electrical entrance. 120/208 1? 3W is definitely permitted at pedestal. Code does not specifically prohibit 208Y/120V 3? 4W at pedestal... but I can tell you that only customized RV would be wired for a 3? supply. See 551.4(A) & (B), 551.31(C), 551.40, 551.42(D), 551.44(D), 551.46(D), and 551.73.
Obviously, voltage drop considerations would differ for a 3? feeder. Jim has indicated using 120/240 service. So I will table further contribution to that discussion until either warranted or solicited.![]()
RV systems are designed for 120/240 supply connection AFAIK. If I had an RV, that's what I'd want to connect to... but given the option of 120/208 or no connection, guess which I'd choose?Why is 551.40 worded the way it is if they didn't intend to prohibit 208/120 volt systems? Again I don't know any great reason to prohibit a 208 volt system in the first place but they kind of excluded them the way they worded things IMO.
Same choice here. For the most part there are no 240 volt loads in them either, I think many units with 50 amp plug still use 120 volt air conditioners, they just have more then one AC and must have more then a 30A 120V supply if you want to be able run all the AC.RV systems are designed for 120/240 supply connection AFAIK. If I had an RV, that's what I'd want to connect to... but given the option of 120/208 or no connection, guess which I'd choose?![]()
Pay particular attention to the nonsense Don pointed out in post 10, in that thread: "It appears that the panel's intent is to permit 120/208 volt systems to serve the line to line loads, but the other code sections were not changed to permit this.":happysad:
That was posted about 7.5 years ago probably has comments based on 2005 NEC and I think the wording is or nearly is identical still in 2014.
Nonsense? Are you drinking?
The ROP he posted clearly shows the CMP intends to allow 208 volt supplies at RV parks.
And by the way, that thread also shows I am wrong at times.![]()
But AFAICT, the mention of 120/240 without including 208 is only for equipment voltage rating, not actual supply voltage. When we do have a 120/208 1? 3W system, we typically use 120/240V rated equipment, do we not?The nonsense is if it is their intention to allow 208 volts, why do they specifically only mention 120 volts and 120/240 volts as the only supply voltages that are permitted?...
Maybe so. What is the danger if one would use a 600 volt fused disconnect instead of a 250 volt fused disconnect in such an application?But AFAICT, the mention of 120/240 without including 208 is only for equipment voltage rating, not actual supply voltage. When we do have a 120/208 1? 3W system, we typically use 120/240V rated equipment, do we not?