Not so,Look deeper into the technical literature on NEC.You would find the same controversy still unresolved.
So post it here so we can all 'know' what you know.
Not so,Look deeper into the technical literature on NEC.You would find the same controversy still unresolved.
........
Not so,Look deeper into the technical literature on NEC.You would find the same controversy still unresolved.
There is no controversy. You are simply mistaken in any belief that there is a safety risk in using an MWBC to serve kitchen countertop receptacles. It is no different at all from using two separate circuits to serve receptacles that are two feet away from each other.You would find the same controversy still unresolved.
There is no controversy. You are simply mistaken in any belief that there is a safety risk in using an MWBC to serve kitchen countertop receptacles. It is no different at all from using two separate circuits to serve receptacles that are two feet away from each other.
Please address my earlier comments, by answering the following question: How can a person be shocked (either at 120V or 240V) by touching a kitchen appliance, unless something inside one or more appliances fails in such a way as to allow an energized wire to contact the external case? My answer is that it cannot happen, that it is a physical impossibility
Please note also that if an appliance does experience an internal failure, then one of two things will be true. Either it will have a ground wire, which means it will trip the breaker and prevent injury,....... the person cannot get shocked.
To T.M. and everybody else.I just said it reduces the likelihood of injury by shock from 240V;it is not possible to eliminate it completly.I hope you see that people use separate receptacles differently from duplex receptacles.
Residential power supplied in India is two wire 240 volts, permitted variation 6%, and maximum load 40 amperes. Frequency 50 Hz. Many power outlets are universal and accept many plugs without adapter. A combination receptacle for types C, D and G is usually present.
I made my statements based on 'Hand book of Electrical design by Mc Partlands'.If you have a copy of it,please go through its second chapter'lighting and appliance branch circuits.You will find support for my statements.
Why do you think that the insulation of a kitchen appliance can not become defective?
Here is a question to make you aware of how complex the situation really is.
Suppose the house wife is touching a metallic grounded kitchen appliance at the moment it is becoming alive due to insulation breakdown.Will she get a shock or not?
[/B]
I don?t have a copy.I made my statements based on 'Hand book of Electrical design by Mc Partlands'.If you have a copy of it . . . .
It can. If it does, then that is the time to throw the appliance in the trash, and buy a new one. That said, if a double-insulated kitchen appliance (e.g., toaster) does experience a failure in its insulation, and also experiences a failure of some internal part that allows the user to get a shock (please note that this is a double failure, and is therefore very unlikely), then the GFCI device into which the toaster is plugged will trip, and the user will not be injured.Why do you think that the insulation of a kitchen appliance can not become defective?
Suppose the house wife is touching a metallic grounded kitchen appliance at the moment it is becoming alive due to insulation breakdown. Will she get a shock or not?
She will get a shock. But then the breaker serving that circuit will trip, terminating the event. The breaker trip will happen so fast that the housewife will likely not feel the shock. Also, the trip will happen so fast that the shock will not cause any damage to her body.
Why do you think that the insulation of a kitchen appliance can not become defective?
Your apprehension is justified.A housewife can be subject to a 240V shock if she is handling two appliances such as dish washer and disposal at the same time in the kitchen and which are connected to that one duplex receptacle.But what to do when the code panel ruled it is safe!
I made my statements based on 'Hand book of Electrical design by Mc Partlands'.If you have a copy of it,please go through its second chapter'lighting and appliance branch circuits.You will find support for my statements.
Why do you think that the insulation of a kitchen appliance can not become defective?
Here is a question to make you aware of how complex the situation really is.
Suppose the house wife is touching a metallic grounded kitchen appliance at the moment it is becoming alive due to insulation breakdown.Will she get a shock or not?
There are facts and there are opinions. It is a fact that the relevant Standard, NFPA 70 (NEC) accepts multiwire branch circuits; it is an opinion whether that is a good idea or not. It is also a fact that they are acceptable as the consensus opinion of the relevant Code Making Panels, the McPartland?s comments notwithstanding.
I made my statements based on 'Hand book of Electrical design by Mc Partlands'.If you have a copy of it,please go through its second chapter'lighting and appliance branch circuits.You will find support for my statements.
...
I don’t have a copy.
She will get a shock. But then the breaker serving that circuit will trip, terminating the event. The breaker trip will happen so fast that the housewife will likely not feel the shock. Also, the trip will happen so fast that the shock will not cause any damage to her body.
If the person is touching the grounded metal part when the ungrounded conductor comes in contact with the metal part, the magnitude of the shock will be limited. The voltage to ground will equal the voltage drop on the EGC....
I am afraid you missed one important point regarding shock hazard.The severity of shock she would experience depends not only on the duration of exposure but also on its magnitude.Sure the time would be limited by the operation of OCPD.But how are you going to limit the magnitude of shock?
210.6 Branch-Circuit Voltage Limitations.
The nominal voltage of branch circuits shall not exceed the values permitted by 210.6(A) through 210.6(E).
(A) Occupancy Limitation. In dwelling units and guest rooms or guest suites of hotels, motels, and similar occupancies, the voltage shall not exceed 120 volts, nominal, between conductors that supply the terminals of the following:
(1) Luminaires (lighting fixtures)
(2) Cord-and-plug-connected loads 1440 volt-amperes, nominal, or less or less than ? hp
The NEC did give consideration to the unique circumstances and the un- qualified individuals working close to electric equipment. It seems to balanced the potential risk of voltages with the use of appliances in a dwelling
If the person is touching the grounded metal part when the ungrounded conductor comes in contact with the metal part, the magnitude of the shock will be limited. The voltage to ground will equal the voltage drop on the EGC.
But still more can be done in the way of safety which may be still within the capability of an Engineer.Watch the discussion with Charlie as it develops,if you really enjoy it.