There is already gfci protection that has a higher leakage threshold , but everything that’s listed in 210.8 requires class A gfci protection and class A protection only has a leakage threshold of 4-6 ma . That’s why cord and plug evse still requires external gfci protection. But the internal ccid that provides the GFPE has a 20 ma threshold which isn’t class A protection. Outdoor hvac equipment will need to be able to operate with Class A protection so the hvac equipment needs manufsctured to tolerate class A gfci protection , they aren’t manufacturing protection with a higher leakage threshold because that wouldn’t be class A