Sauna GFCI?

Merry Christmas
That would be an AHJ call, where I am in Oregon the state amended the 210.8(F) to read:

So it would not be required here anyway.

You’re definitely right 90.4(b) definitely leaves that decision up to the Ahj, was just saying what I felt was the intent behind the code . Luckily for you that never had to even cross your mind lol


Sent from my iPhone using Tapatalk
 
Luckily for you that never had to even cross your mind lol
What did cross my mind is that it takes a decent amount of fault current around 120 Amps to trip a 40A regular breaker (300% of the breaker) in a short time like a few seconds, and a 39A ground fault could flow indefinitely.
So I get why all the codes in the world have been pushing for some improvement there.
 
I thought so but that was a long time ago lol, I was replying to post 73 with my question,
what are your feelings on post 73? Do you feel 210.8(f) would be applicable or are you in agreement with his post ?
I'm didn't go back an look but pretty certain I answered this question early on in the thread.

IIRC I said something to the effect that if this outdoor item is a free standing utilization equipment. other than most lighting outlets NEC requires GFCI protection via 210.8(F) in the last two NEC editions. If it considered a building/structure with the outlet inside - it may still require GFCI but would be something other than 210.8(F) that would require it.
 
I'm didn't go back an look but pretty certain I answered this question early on in the thread.

IIRC I said something to the effect that if this outdoor item is a free standing utilization equipment. other than most lighting outlets NEC requires GFCI protection via 210.8(F) in the last two NEC editions. If it considered a building/structure with the outlet inside - it may still require GFCI but would be something other than 210.8(F) that would require it.
If it’s considered a seperate building or structure why wouldn’t you consider it to fall under the scope 210.8(f)’s requirement to protect these outlets located in accessory building on the dwellings property. He said its the size of a smaller detached shed.
 
If it’s considered a seperate building or structure why wouldn’t you consider it to fall under the scope 210.8(f)’s requirement to protect these outlets located in accessory building on the dwellings property. He said its the size of a smaller detached shed.
Because (F) is for outdoor outlets. If it is considered to be indoors in a dwelling accessory structure (A) is what would apply to it, and (A) only applies to receptacle outlets which would not apply if the sauna were hard wired connection. Sauna is not mentioned in the list of specific appliances of (D) either.
 
Because (F) is for outdoor outlets. If it is considered to be indoors in a dwelling accessory structure (A) is what would apply to it, and (A) only applies to receptacle outlets which would not apply if the sauna were hard wired connection. Sauna is not mentioned in the list of specific appliances of (D) either.

64e27f67462790e8074e725f9ae0625b.jpg

It says (f) requires gfci protection for all outdoor outlets other than those covered in 210.8(a), exception 1, including outlets installed in the following locations and I circled those following locations . They say all outlets other than the receptacle outlets covered by 210.8(a) . A Hardwired outlet is not a receptacle outlet so (a) does not cover it so it falls under (f)


Sent from my iPhone using Tapatalk
 
If you have not seen a barrel sauna they are pretty interesting here is an example of one:
View attachment 2575549
I’ve seen plenty of barrel saunas and wired a few . I only used that example because he said it couldn’t be an accessory building but that’s up to interpretation and then he said (a) covers the location so (f) says it doesn’t apply but that’s not what (f) says it doesn’t apply to the receptacles outlets that are already covered by (a) hardwired connection/outlet isnt covered by (a) because it’s not a receptacle outlet location is irrelevant. Not trying to be snappy sorry if it comes off that way
 
64e27f67462790e8074e725f9ae0625b.jpg

It says (f) requires gfci protection for all outdoor outlets other than those covered in 210.8(a), exception 1, including outlets installed in the following locations and I circled those following locations . They say all outlets other than the receptacle outlets covered by 210.8(a) . A Hardwired outlet is not a receptacle outlet so (a) does not cover it so it falls under (f)


Sent from my iPhone using Tapatalk
My bad. I should have read through (F) before replying. My state amended 210.8 to be mostly the same as it is in 2017NEC so I don't necessarily deal with (F) for work I do.
 
All good bro appreciate you saying that , most guys usually just double down , respect !! But that makes sense !
Most of us on here go by what we call 'Charlie's Rules';
I lost track of how many times I have read the code then to re-read it and find it says something other than what I always thought it said.
I’ve seen plenty of barrel saunas and wired a few .
Do you always put them on a GFCI in Mass?
 
Most of us on here go by what we call 'Charlie's Rules';
I lost track of how many times I have read the code then to re-read it and find it says something other than what I always thought it said.

Do you always put them on a GFCI in Mass?
Absolutely not, mass deletes 210.8(f) , I try to to base all my comments on what the NEC requires, and refrain from making comments based on the requirements of my locally adopted electrical code, or at least address that it’s in reference tothe mass code if I do . This is strictly what I believe to be the intent behind the code in the NEC i
 
My bad. I should have read through (F) before replying. My state amended 210.8 to be mostly the same as it is in 2017NEC so I don't necessarily deal with (F) for work I do.
Btw my state deleted 210.8(f) as well so providing gfci protection for that sauna or any other outdoor hardwired utilization equipment unless required by 210.8(d) would never cross my mind either lol
 
Most of us on here go by what we call 'Charlie's Rules';
I lost track of how many times I have read the code then to re-read it and find it says something other than what I always thought it said.

Do you always put them on a GFCI in Mass?
And I often find myself applying “Charlie’s rules” as well. Mostly when a credible/knowledgeable source has a different interpretation of a codes intent than I do, and just like you multiple times after re reading the rule in question I’ve felt that the intent of the code is different then I previously believed it to be
 
My bad. I should have read through (F) before replying. My state amended 210.8 to be mostly the same as it is in 2017NEC so I don't necessarily deal with (F) for work I do.
The word "in" was not the correct word as the section is only intended to apply to outside outlets. "In" will be replaced with "at" in the 2026 code to clear up the confusion.
 
The word "in" was not the correct word as the section is only intended to apply to outside outlets. "In" will be replaced with "at" in the 2026 code to clear up the confusion.
Very good point , which would lead to an outlet located inside the barrel sauna whether it was considered to be an accessory building or not , would not fall under the scope of 210.8(f) correct ?
 
Btw my state deleted 210.8(f) as well so providing gfci protection for that sauna or any other outdoor hardwired utilization equipment unless required by 210.8(d) would never cross my mind either lol
I had the air conditioner units on my mind as that was one the biggest problematic things with this requirement, but did know it included all outside outlets other than the mentioned lighting outlets in the wording and/or exception but for some reason did not think about interior of dwelling accessory buildings/structures though I'm sure I was aware of it applying there at one time, just haven't been required to do so yet.
 
The word "in" was not the correct word as the section is only intended to apply to outside outlets. "In" will be replaced with "at" in the 2026 code to clear up the confusion.
Are you talking about "in" accessory buildings? changing to "at" accessory buildings - meaning on the exterior?
 
I had the air conditioner units on my mind as that was one the biggest problematic things with this requirement, but did know it included all outside outlets other than the mentioned lighting outlets in the wording and/or exception but for some reason did not think about interior of dwelling accessory buildings/structures though I'm sure I was aware of it applying there at one time, just haven't been required to do so yet.
It looks like they plan on incorporating sp gfci protection for listed hvac equipment once the tia expires and seeing either class A or SP GFCI protection as acceptable . I wonder if there are conditions as to which one will be acceptable based on the load pf the equipment may Don can provide clarity
 

Attachments

  • IMG_1135.png
    IMG_1135.png
    600.2 KB · Views: 1
Top