Have you tried doing a functional test? Put the system into alarm for 5 minutes and see where the batteries are at. If possible do a 24 hour battery test. I assume your battery calcs are correct.
 

zog

Senior Member
Location
Charlotte, NC

nhfire77

Senior Member
Location
NH
No, it measues Z. Have you looked at IEEE Std 450 for testing requirements for SLA batteries?

No, but I have read NFPA 72. It requires full load testing, and allows for simulated loads. I am on the road without a book to reference a section.

Is that standard available for free?
 

zog

Senior Member
Location
Charlotte, NC
No, but I have read NFPA 72. It requires full load testing, and allows for simulated loads. I am on the road without a book to reference a section.

Is that standard available for free?

No, like all real standards you have to buy it, which in turn pays for all the R&D that goes into the standards.
 

nhfire77

Senior Member
Location
NH
No, like all real standards you have to buy it, which in turn pays for all the R&D that goes into the standards.

Any chance you would quote the sections you are referring to, I cannot justify buying something like that for this situation.
 

zog

Senior Member
Location
Charlotte, NC
Any chance you would quote the sections you are referring to, I cannot justify buying something like that for this situation.

Bascially the entire document would need to be posted, I really don't have the time to type up 150 pages of stuff. I suggest you contact a testing company in your area, most NETA testing companies will have the expertise and equipment to do this type of thing. www.netaworld.org
 