I have a customer that's building a detached garage 50ft. from his existing home. Customer already bought 1-1/2 in. PVC conduit and 2/2/2/4 SER Aluminum cable with and outer sheath.
I told him the NEC doesn't allow SER cable to be installed in PVC conduit buried under ground. He really wants to use this cable since he allready bought it.
I tried looking up the code reference but couldn't find anything that prohibits this.
Is SER cable allowed to be installed in PVC conduit buried underground?
If not what's the code reference that prohibits this installation?
I generally install USE-2 without an outer sheath in underground PVC conduit for this type of installation.
What aluminum cable types do others use for this type of installation.