wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
California has not amended 230.70(A)(1).
Cheers, Wayne
Cheers, Wayne
California has not amended 230.70(A)(1).
Cheers, Wayne
Can you tell me the CEC section that allows this or is basically a CA custom?
Most places that allow service conductors beyond the first readily accessible place have a defined length.
The NEC definition of outside concerning service conductors was already given, 230.6.
I sympathize dude, but I see no way that your argument will prevails. Sorry.
Regarding 230.6, it is a misconception that the NEC requires service conductors to be outside of a building. Please see this post:
http://forums.mikeholt.com/showthread.php?t=194178&p=1949378#post1949378all
If 230.6 were to mean that all service conductors must be outside, then 230.70 would not implicitly allow them by regulating how long they can run through the inside of a building. Why would 230.70 exist in its current form? It would be regulating a situation that is already forbidden by 230.6. Additionally, 230.6 is under "I. General" and applies to ALL service conductors. It makes no distinction between overhead and underground service conductors. But section 230.32 says
"[Underground] Service conductors entering a building or other structure shall be installed in accordance with 230.6 or protected by a raceway wiring method identified in 230.43."
The "or" makes it clear that you are allowed to install underground fed service conductors, in a raceway like EMT (as per 230.43) without concrete encapsulation after they enter a building. If this is the case, then 230.6 cannot mean that all service conductors must be outside.
Regarding 230.70, I've explained in these two posts that this code section does not forbid a mast running horizontal inside of a building
http://forums.mikeholt.com/showthread.php?t=194172&p=1949272#post1949272
http://forums.mikeholt.com/showthread.php?t=194172&p=1949471#post1949471
Basically what I'm saying is this. The code does not forbid service conductors from entering a building, it doesn't forbid service conductors from running horizontally through a building, and it doesn't specify a maximum length of run when inside. It is not a "California custom", it is allowed by the code. All I'm asking is that someone actually show me how my reasoning in any of these posts is flawed.
being "nearest the point of entrance" cannot be interpreted literally to an extreme.
It can be interpreted to an extreme by an AHJ. Since "nearest the point of entrance" does not mention a length, it can be interpreted in almost any way by the AHJ.
It can be interpreted to an extreme by an AHJ. Since "nearest the point of entrance" does not mention a length, it can be interpreted in almost any way by the AHJ.
So if you have a conduit with service entrance conductors coming up out of the footing of a house inside an exterior wall for 30" and then it enters the bottom of a flush mount meter combo panel and an inspector turns it down, not on the grounds that it is inside the building, but because it is not "nearest the point of entrance" you say that inspector is adhering to the intent of the code?
Incorrect, the crawl space is not readily accessible, so if the pipe goes through/under a footing and immediately turns up into a panel/disco inside a wall and terminates in there, the NEC is satisfied.
It can't do that. It needs to come up outside the wall or be wrapped in concrete. California is the only place in the country where service conductors are allowed to be installed inside a wall.Can you clarify? I didn't mention a crawlspace. Perhaps in your area most homes are raised floors with crawlspaces underneath? I'm speaking about a home built directly atop a concrete slab, no crawlspace underneath. The conduit riser comes up vertically through the footing, through the bottom plate of the wall, runs for 30" in the wall, then terminates in the bottom of the meter panel. I've attached a drawing showing what I'm talking about.
Can you clarify? I didn't mention a crawlspace. Perhaps in your area most homes are raised floors with crawlspaces underneath? I'm speaking about a home built directly atop a concrete slab, no crawlspace underneath. The conduit riser comes up vertically through the footing, through the bottom plate of the wall, runs for 30" in the wall, then terminates in the bottom of the meter panel. I've attached a drawing showing what I'm talking about.
So if you have a conduit with service entrance conductors coming up out of the footing of a house inside an exterior wall for 30" and then it enters the bottom of a flush mount meter combo panel and an inspector turns it down, not on the grounds that it is inside the building, but because it is not "nearest the point of entrance" you say that inspector is adhering to the intent of the code?
It can't do that. It needs to come up outside the wall or be wrapped in concrete..
That install would be legal.
Or the inspector may just decide that the disconnect is nearest the point of entrance and allow the situation you describe. It is up to the inspector unless local amendments apply.
So my question to you would be, if an inspector quoted 230.70 and said that the disco was not "nearest point of entrance" because the pipe runs for 30" inside the wall before terminating he would not be within his rights? He would be wrong?