Taping a neutral on a 3 wire range or dryer circuit is only of use in the panel from which the 3 wire branch circuit originates. That still does not address the underlying problems arissing out of such installations remaining in service once the panel it originates in is no longer the Service Equipment. The frame of the appliance will be bonded to the Grounded Current Carrying Conductor (Neutral) if that appliance was properly installed in the first place. Metal reinforced water supply hoses, contact with an adjacent appliance, or being on a conductive floor, such as concrete, if the legs are conductive will all provide a sneak current pathway for neutral current to flow over exposed conductive surfaces. The controls of a range and the motor and controls of a clothes dryer all require a 120 volt supply. In both cases that guarantees that there will be current flowing on the Grounded Current Carrying Conductor (Neutral). As long as the connections of the Grounded Current Carrying Conductor (Neutral) remain in good condition most of the current from the 120 volt portion of the load will return on the Grounded Current Carrying Conductor (Neutral). If any connection of the Grounded Current Carrying Conductor (Neutral) becomes high resistance for any reason that current will be looking for a way back to the windings of the secondary of the transformer from whence it came that was never intended to carry electrical current. It is nearly inevitable that the leakage pathway will have considerable voltage drop and that the touch potential of some conductive surfaces will become dangerous.