Quick question - Any issues code or otherwise with the main service panel being in the garage of a house?
NO.....on neither if the install is done correctly.Quick question - Any issues code or otherwise with the main service panel being in the garage of a house?
Section 230.70(A)(1) permits the Service Disconnection Means to be located outside of a building and when necessary Section 230.40 Ex.3 can assist......it does not specify where outside of that building....others are sure to disagree but thats their prerogative.
I have seen plenty of million dollar homes that had the service for the home in the detached garage with feeders to remote distribution panels in the dwelling structure and have never seen one fail because of it.
Outside of the building is one thing, in or on a separate structure is another, if the only purpose of the structure is to provide support for the equipment - we can argue this for hundreds of posts, but a detached garage is a separate structure to most competent electrical professionals.
Are you suggesting the property monetary value has an impact on the rules with that last statement?
I can't say inspectors here would let it go because I haven't tried to slip this one past them, but am assuming they wouldn't let it go. A garage that has a "breezeway" connecting it to the house is likely considered all one building.
I don't see how 230.40 exception 3 fits into this discussion at all.No you are suggesting it...I am saying that is where I witnessed it the most.....due to the layout of the properties. Your "interpretation" of where the "outside" limit should be is not founded in the NEC so...If you notice in Section 230.40 Ex. 3....the dog waggin the tail does not matter which end the tail is located on.......now lets assume THAT analogy....
But just to be clear, you would approve a *service* disconnect 50 ft. from the building as long as there was also a non-service disconnect at the building?edit to add:
I would approve a service disconnect attached to a building. I would not approve a service disconnect 50 ft from a building.
I would think comparing 225.32 location and 230.70 (A) (1) location the building disconnect location has to be closes to where the supply conductors enter the building even if the disconnect is outside of the building.
You may argue that 230.70 is not clear that the exterior disconnect has to be close to where the service entrance enters the building but you cannot argue the same for 225.32 location.
I think from these two sections it can be concluded that a disconnect inside and a disconnect outside needs to be close to where the supply conductors enter the building.
edit to add:
How about 30'.........do you not observe Section 550.32(A) as well?..which clearly has a defined maximum limit.....which is not expressed in 230.70(A)(1).....we can agree to disagree.
That exception allows us to run service entrance conductors to both structures (for the single family dwelling and accessory buildings in this application) from "a single service drop, set of overhead service conductors, set of underground service conductors, or service lateral."
Maybe I missed something but I thought this discussion was about service equipment in/on the accessory building/structure and branch circuits run to the other building/structure.
I recognize 90.3 in fairness you are referencing special provisions found in article 550 which mandates the building be supplied by a feeder to a main in a distribution panel in the dwelling
Edit:
You indicated others would disagree with you that the location of an exterior disconnect was not required at the building location or as you put it at any specified location. As you predicted some here are going to disagree