Nikola Tesla said:WOW!
We wouldn't get away with using 2/0 for 200 amp service here!
Why not, it's perfectly legal for a residential service if you are installing per the NEC.
Roger
Nikola Tesla said:WOW!
We wouldn't get away with using 2/0 for 200 amp service here!
kid_stevens said:3/0 no derating allowed here by PNM on Service entrance connectors.
310.15(B)(6)
(6) 120/240-Volt, 3-Wire, Single-Phase Dwelling Services and Feeders For individual dwelling units of one family, two-family, and multifamily dwellings, conductors, as listed in Table 310.15(B)(6), shall be permitted as 120/240-volt, 3-wire, single-phase service-entrance conductors,
Nikola Tesla said:WOW!
We wouldn't get away with using 2/0 for 200 amp service here!
220/221 said:I was careful. I feel the worst that could have happened would be to scare the crap out of me and kick some big fuses somewhere and put out a few neighbors.
celtic said:Even if it's CU conductors? [T310.15(B)(6)]
Why not?
Nikola Tesla said:The original post didn't say CU, I just assumed AL because that's what we mainly use around here.
Nikola Tesla said:around here.
bradleyelectric said:Where's that?
Nikola Tesla said:The original post didn't say CU, I just assumed AL because that's what we mainly use around here.
nyerinfl said:Assumed AL? 110.5 tells us to assume copper!
This is a stand alone article section that allows the ampacity of the conductors in a specific application and as listed in Table 310.15(B)(6).
I did not think Delaware was that big I could wire the whole state in a month.markabbottjr said:I'm in Delaware and i specialize in service upgrades.I do on average of 2 to 3 per day,3 to 4 if all local,i have one man that works for me and we are both on the job and we are really fast and each job ranges from $1300.00 to $2000.00 depending on distance traveled.Most of my jobs require a disconnect with meter so it also depends on how much 4/0 SER is used.We all know how fun that is to buy everyday.
St.Louis Mo areabradleyelectric said:Where's that?
markabbottjr said:I do on average of 2 to 3 per day,3 to 4 if all local.... it also depends on how much 4/0 SER is used.We all know how fun that is to buy everyday.
markabbottjr said:I'm in Delaware and i specialize in service upgrades.I do on average of 2 to 3 per day,3 to 4 if all local,i have one man that works for me and we are both on the job and we are really fast and each job ranges from $1300.00 to $2000.00 depending on distance traveled.Most of my jobs require a disconnect with meter so it also depends on how much 4/0 SER is used.We all know how fun that is to buy everyday.
emahler said:that sounds like blood money...i can't fathom doing more than 2 service changes in 1 day...and doing 2 would be a long day...average service change around here is overhead with minimum 20 ckts...heck it takes an hour or more just to label the panels...
what kind of services are you doing to average 2-3 a day?
Nikola Tesla said:The original post didn't say CU, I just assumed AL because that's what we mainly use around here.