Pierre C Belarge said:
al hildenbrand said:
Given that the heat concentrates at the connections and internal breaker contacts, the end-of-life scenarios will most likely include the catastrophic failure of those connections / contacts with load current sustained series arcs, that the AFCI electronics, we are assured by UL, will NOT detect because the arc current is not exceeding the 50 to 70 amps trigger threshhold.
That's assuming the electronics are, in fact, still viable at the end of this heat degradation cycle.
Al
Where did you get that information from?
Pierre,
The information I base my opinion on is the result of my personal experience, not exclusively with AFCIs, but also with the existing installations that have failed or are failing, that I have repaired, replaced or examined.
Most recently, I have removed a 1978 Gould 100 A 2-pole service disconnect breaker in a 16-pole panel that was at the erratic end of being consumed by a burning lug and an internal contact burning.
The homeowner called me to his dwelling to troubleshoot a GFI receptacle that he had just installed that he was certain was messing up the house. I got there, and as he described the extent of the sporadic and spread out lack of power, I realized I wanted to see the panel rather than look at the GFI and its j-box. As we went through the house and down to the service center, the HO realized that the power was out again (partially, as it had been many times before).
When we got to the panel, before I could react, he reached up to the 100 A disconnect, shut it off, and turned it back on. The basement light behind us came on for the first time.
In this particular instance, the #2 Al SE conductor on the left pole of the disconnect breaker had been heating badly enough to have over two inches of #2 Al stranded conductor melted
clean of insulation. The heat, created in the resistance of the failing terminal lug, had also been conducted into the breaker and was adding to the heat normally created in the internal breaker contacts. Over the many months that this heating and cooling, under varying load, had been happening, the contacts inside the breaker on its left side had degraded and the contact resistance was rising.
When I closely examined the breaker, the bakelite case was starting to discolor and crack like a drying out riverbed mud field. This cracking was local at the internal contacts of the breaker. Other bakelite damage was occurring by the terminal lug.
The resistance of a lug or terminal or contacts, once it starts to rise enough, will cause small incremental increases in the resistance of the splice. With each increase in resistance, the amount of heat created will increase. This can be a gradual process until the amount of heat created exceeds the heat that can be conducted, convected and/or radiated away. The heat concentrates, with attendant temperature spiking and catastrophic effects ensue.
Pierre, if this same process of heat degradation of contacts and splices occurs in a breaker with AFCI electronics, in my opinion, the electronics will stand an excellent chance of having been turned into green goo by the heat, long before the runaway temperature spikes start occuring.
But, if the electronics happen to survive to the end, they won't help because the heating and burning of the contacts, under load, are going to be only at load, not short circuit currents. The branch/feeder AFCI will ignore currents below 50 to 70 Amps.
If the occupant of a building with a breaker starting into the catastrophic end cycles of heat concentrations exceeding "black body radiation limits" is content to keep resetting the breaker, rather than call in a professional, then the conditions are present for property loss, injury or death.