So the spec looks to me as if we are allowed to share neutrals. Agree? Would need a circuit breaker handle tie, correct?
Thanks.
So the spec looks to me as if we are allowed to share neutrals. Agree? Would need a circuit breaker handle tie, correct?
Thanks.
EGC... no, assuming we are discussing a grounded neutral here. Required upsizing of the EGC is contingent upon the size of the ungrounded circuit conductors being greater than the minimum sufficient size.... Wouldnt the ground need upsizing as well? ...
If the circuits don't have voltage between them the we are not talking about MWBC to begin with.
Jap>
Which would be the case if 2 or more circuits were on the same phase, in which case your not dealing with a MWBC by definition.
JAP>
The spec doesn't specifically say the two or three ungrounded conductors are of differing phases. jap is being pedantic... but FWIW, the spec' is ambiguous (defeating the purpose of a spec') and brings it out of people that must be oriented to detail to do good work.Ok but how is that related to what MrLucky posted?
The spec doesn't specifically say the two or three ungrounded conductors are of differing phases. jap is being pedantic.
"Circuits where two or three phases share a single conductor neutral."
Two or three A phases... or maybe B phases... could even be C phases... then again perhaps A and B... maybe B and C... ah heck, let's just make 'em ABC.I think that we all know what is meant by "Circuits where two or three phases share a single conductor neutral."
How is this not a MWBC?
Two or three A phases... or maybe B phases... could even be C phases... then again perhaps A and B... maybe B and C... ah heck, let's just make 'em ABC.
Yes, ambiguous.
Two or three A phases... or maybe B phases... could even be C phases... then again perhaps A and B... maybe B and C... ah heck, let's just make 'em ABC.
Yes, ambiguous.