200.4 Neutral Conductors. Neutral conductors shall be
installed in accordance with 200.4(A) and (B).
(A) Installation. Neutral conductors shall not be used for
more than one branch circuit, for more than one multiwire
branch circuit, or for more than one set of ungrounded
feeder conductors unless specifically permitted elsewhere
in this Code.
(B) Multiple Circuits. Where more than one neutral conductor
associated with different circuits is in an enclosure,
grounded circuit conductors of each circuit shall be identified
or grouped to correspond with the ungrounded circuit
conductor(s) by wire markers, cable ties, or similar means
in at least one location within the enclosure.
Exception No. 1: The requirement for grouping or identifying
shall not apply if the branch-circuit or feeder conductors
enter from a cable or a raceway unique to the circuit
that makes the grouping obvious.
Exception No. 2: The requirement for grouping or identifying
shall not apply where branch-circuit conductors pass
though a box or conduit body without a loop as described
in 314.16(B)(1) or without a splice or termination.