2.8.2.3 Sprinkler systems conforming to NFPA 13or the NBCC, whichever is applicable (see Part 9), shallbe permitted to be installed in the hoistway, machineroom, and machinery spaces, subject to the requirementsof 2.8.2.3.1 through 2.8.2.3.4.
2.8.2.3.1 All risers and returns shall be locatedoutside these spaces. Branch lines in the hoistway shallsupply sprinklers at not more than one floor level. Whenthe machine room is located above the roof of the build-ing, risers, return pipes, and branch lines for the machineroom sprinkler(s) shall be permitted to be located in thehoistway between the top floor and the machine room.
2.8.2.3.2 In jurisdictions not enforcing the NBCC,means shall be provided to automatically disconnect themain line power supply to the affected elevator uponor prior to the application of water from sprinklerslocated in the machine room or in the hoistway morethan 600 mm (24 in.) above the pit floor. This meansshall be independent of the elevator control and shallnot be self-resetting. The activation of sprinklers outsideof the hoistway or machine room shall not disconnectthe main line power supply.
2.8.2.3.3 Smoke detectors shall not be used toactivate sprinklers in these spaces or to disconnect themain line power supply.