Installing a 480 single phase service for roadway lighting. Not familiar with 480 single phase. any pointers?
Light fixture ballasts don't care about one wire or two wire.
Can I assume that you mean that ballasts do not care if it two hot wires or one hot and one grounded/neutral for the 480V?
That would be two phases of a 3 phase system. Otherwise it is not an ANSI recognized system voltage. As such, it is supplied by a two pole breaker(preferred) or two fuses, controlled by two pole contactor.
It is one leg 480 volt to ground. 1 single pole breaker.
While not the majority of 480V systems, it is not so unusual to find single phase, 480V derived from a non three phase system at some of the farms our shop does work for.That would be two phases of a 3 phase system. Otherwise it is not an ANSI recognized system voltage. As such, it is supplied by a two pole breaker(preferred) or two fuses, controlled by two pole contactor.
While not the majority of 480V systems, it is not so unusual to find single phase, 480V derived from a non three phase system at some of the farms our shop does work for.
The POCO does not mind using a different transformer and the farmer likes not having to pay for the expense of bringing three-phase all the way out to his hay field.
I have never seen a 1 phase 480v Hot & Neutral in use.My involvement has always been 3 phase distribution and lights connected phase to phase with fuses oft times in pole base handhole as LW says.
dick
I have never seen a 1 phase 480v Hot & Neutral in use.My involvement has always been 3 phase distribution and lights connected phase to phase with fuses oft times in pole base handhole as LW says.
dick
While not the majority of 480V systems, it is not so unusual to find single phase, 480V derived from a non three phase system at some of the farms our shop does work for.
The POCO does not mind using a different transformer and the farmer likes not having to pay for the expense of bringing three-phase all the way out to his hay field.
Only place you will see this is in Highway lighting systems. Traffic signals will be 220
My point was that it is NOT an ANSI recognnized voltage. The OP did NOT say anything about this being a Utility Service, in which case all bets are off as far as ANSI concerned, with certain exceptions where all MAJOR Utilities DO follow the ANSI Standard and the few, who still does not, does so for legacy reasons, mainly, and they are stuck with it.
If you come to where I live, I can take you for a little drive and show you many 240/480 single phase services in remote areas supplied by single phase primary lines from POCO. Majority of them supply irrigation equipment, and they use rotary phase converters to derive three phase. These systems only require 10 KVA max and a phase converter is the less costly way to go vs. having POCO supply a full three phase bank or even an open delta bank, plus additional primary conductors for what would be pretty long runs.
If you come to where I live, I can take you for a little drive and show you many 240/480 single phase services in remote areas supplied by single phase primary lines from POCO. Majority of them supply irrigation equipment, and they use rotary phase converters to derive three phase. These systems only require 10 KVA max and a phase converter is the less costly way to go vs. having POCO supply a full three phase bank or even an open delta bank, plus additional primary conductors for what would be pretty long runs.
They could have a 480 volt corner grounded delta source also.