electrofelon
- Cherry Valley NY, Seattle, WA
- Electrician
(3 sqrt2 Vll) / Pi
basically the wave form integrated and averaged
Right, there it is. I knew the 1.35 value but couldnt remember the algebraic form.
(3 sqrt2 Vll) / Pi
I think you meant irrelevant... but it actually is relevant... because if (which is a big IF according to the info' I gleaned from light research) the output is sinusoidal and balanced, that means the output is linear... and input power (minus losses) follows the output power.Most do but that's altogether relevant to the topic since it's the input that is being considered
I think you meant irrelevant...But doesn't mean it is linear.You might consider "not altogether relevant" in that way. No big deal
And the thread isn't about input power anyway,
69/26.4 = 2.6![]()
So I guess your answer to my earlier question is, "Never talk about the relationship of input current to motor current on a 3 phase VFD fed by a single phase source, because you have no way of knowing exactly what it will be since it is a non-linear system; it's unknowable." Is that right? :blink:
I think I'll just try to skirt the subject to avoid sounding pedantic (or more pedantic than I already sound to most electricians), and simply stick to telling them to double the current rating of the VFD to the motor FLA and leave it as a DC bus ripple issue, since that's a better reason anyway. Then when they ask me what the input current will be, I'll tell them I have no way of knowing; could be 1.5x, could be 2.43x, could be 1.732x, who knows...![]()
Power in = power out less lossesYou might also consider changing your replies when asked what the 3 phase input current is to a VFD. Since it is also the exact same harmonic rich non linear incalculable waveform as 1 phase input, just adding 2 more humps to the total. If 1 phase input current is an unknown, so must be the identical 3 phase current input. And certainly stop trying to relate power in to power out in either system.
Generally the output current is a close approximation to a sinewave because of the chopping frequency (typically a few kHz) and the smoothing effect of load inductance.and the output fundemental better contain >95% of the power or the motor would run at an indeterminate speed
You said the same about my post that basically said the same thing as Ingenieur's. Perhaps you should read the thread title. It appears you cannot make the correlation between output and input currents.Generally the output current is a close approximation to a sinewave because of the chopping frequency (typically a few kHz) and the smoothing effect of load inductance.
But that isn't what the topic is about.
Correct. Unless you know component values and do the appropriate calculations. There is no one size fits all magic conversion factor.You said the same about my post that basically said the same thing as Ingenieur's. Perhaps you should read the thread title. It appears you cannot make the correlation between output and input currents.
Do we not know for a fact the RMS input current cannot be less than the square root of 3 times the RMS output current?Correct. Unless you know component values and do the appropriate calculations. There is no one size fits all magic conversion factor.
Jraef's premise in this thread is that the diode current is equal sqrt(3) times output current.Do we not know for a fact the RMS input current cannot be less than the square root of 3 times the RMS output current?![]()
I did not see the other thread before it got gutted but did you show an example calc where the input current does not equal output current times sqrt(3)?Correct. Unless you know component values and do the appropriate calculations. There is no one size fits all magic conversion factor.
Yes.Do we not know for a fact the RMS input current cannot be less than the square root of 3 times the RMS output current?![]()
Diode current? I thought it was input current.Jraef's premise in this thread is that the diode current is equal sqrt(3) times output current.
I thought we were talking about sizing a VFD, i.e. its input current rating so as to effectively power a motor up to FLA. I think input current when the motor is not fully loaded is trivial in that pursuit.Yes.
For both you and Mivey.
Simple example.
On no load, a typical cage induction motor runs at about 30% FLC. Say 30A for a 55kW, 400V motor. The input current in such circumstances is very much lower. Certainly under 10A.
I was simply giving an example, one on the limits, of why you can't use a fixed conversion factor.I thought we were talking about sizing a VFD, i.e. its input current rating so as to effectively power a motor up to FLA. I think input current when the motor is not fully loaded is trivial in that pursuit.