Carultch
 - Massachusetts
In order for inverters to grid-form a WYE grid, you have to connect them in a WYE manner, or have a delta:wye transformer to form the neutral. Either directly through a delta:wye transformer, or indirectly with an auxiliary delta:wye transformer used as a grounding bank. Usually the latter is a more economical way of doing it.If we consider these two circuits as totally independent (not grid-connected), would it take (4) of the wye circuits, each with (3) 240 volt voltage sources, to come close to the same energy as the (1) delta with (3) 240 volt voltage sources?
The reason is that grid-forming inverters have to establish the voltage-to-ground of all three phases. This is not possible to do directly with inverter power stages connected in a delta formation. A delta formation can establish interphase voltage, but it can't establish where relative to the neutral point, the voltages are.
Most grid-tied inverters are grid-following, rather than grid-forming, which means they do not produce an independent voltage source. In an ideal textbook model of the grid, they'd be current sources. UL standards require that inverters stay off during a power outage, unless there is an air gap between the inverter and the public utility grid. In other words, a transfer switch that keeps the power and voltage on the customer's property, for the safety of the utility linesmen.