Re: Single phase load on 208/120Y calculation req'd by Oreg
Hi All, I was finally able to perform the experiment on a 120/208 Y system today. We used a 29.725 ohm resistor from an old load bank as a load. according to the calculations this should develop a load of 1455va connected to 208 volts.
an actual voltage of 204 volts was available at the panel. On attaching the load and energizing the circuit, a current flow of 6.9 amps on a Fluke 33 true RMS meter was read.
204v* 6.9A =1407.6va OK so far.
calculate va from load resistor and 204v
204v /29.725ohms =6.86A (read 6.9 on meter)
204v*6.86A =1400va of load Looks pretty close to me.
no factor of ((2/3)*sqr(3))had to be used to calculate the amperage through the load. This was a pure resistive load so no voltage vs current phase shift more than the normal transformer inductive loading occured.
It is always nice to have the reality back up the theory and vice-versa. Now we know. Just use the normal ohms law calculations for ANY single phase load, whether its on a true single phase transformer or on a combination of 3 phase windings.
Garrett
Hi All, I was finally able to perform the experiment on a 120/208 Y system today. We used a 29.725 ohm resistor from an old load bank as a load. according to the calculations this should develop a load of 1455va connected to 208 volts.
an actual voltage of 204 volts was available at the panel. On attaching the load and energizing the circuit, a current flow of 6.9 amps on a Fluke 33 true RMS meter was read.
204v* 6.9A =1407.6va OK so far.
calculate va from load resistor and 204v
204v /29.725ohms =6.86A (read 6.9 on meter)
204v*6.86A =1400va of load Looks pretty close to me.
no factor of ((2/3)*sqr(3))had to be used to calculate the amperage through the load. This was a pure resistive load so no voltage vs current phase shift more than the normal transformer inductive loading occured.
It is always nice to have the reality back up the theory and vice-versa. Now we know. Just use the normal ohms law calculations for ANY single phase load, whether its on a true single phase transformer or on a combination of 3 phase windings.