Re: Single phase load on 208/120Y calculation req'd by Oreg
I will take a chance and see if this will format the same using cut and paste from a Microsoft Word Document. If not, maybe someone can help me with being able to take my document and put it on this forum so that it makes sense.
I am of the opinion that there are four ways to do this problem at the very minimum! The method that some writers use is to take the total vA load of all three phases totaled together and divide by 1.732 X 208. If you have a totally balanced load, no problem but this is highly unlikely.
The second method I see a lot is to take phase A as a worse case scenario and apply the line to neutral on phase A and N, the line to line single phase load on line A & B, and the three phase load and apply to A, B & C. Then they total up the phase A load and this will be the worse possible case without balancing the system and divide that vA load by 120 volts. While this is much easier and quicker, it is not the most accurate and in some cases it would require a larger service than necessary to meet Minimum NEC requirements.
The third method is to monkey around with incorrect math trying to equate the difference between 208 and 230 volts when calculating the single phase 208 volt loads but the fact remains that this is comparing apples with oranges. There is no relationship between 120 volt or 240 volts in a line to line 208 volt load. While I am not a vector math person, I have friends that are and we are convinced that the phase shift between the delta primary and the wye secondary does not change the fact that a single phase line to line load is a direct result of turns ratio. A 6,000 vA load is a 6,000 vA load if it is rated at 208 volts. When you apply to a different voltage then you have to determine the resistance of the load and if my memory is correct take the voltage squared over the resistance to fine the new volt-ampere rating.
In 1990 the NEC first showed a 208 volt column in Table 430.148 and prior to this time we had to make an adjustment for the currents listed in the 230 volt column when we were using a 208 volt motor.
The more I look at what the State of Oregon is doing, they are trying to make an adjustment to make the answers on a sheet of paper comparing the amp method to the volt-ampere method, work out correctly.
The more I play with these numbers the more I am convinced that the following method is to be used.
Calculate the following loads:
2 ? 15 kW heating units ? 3 phase 208v
1- 8 kW water heaters ? 3 phase 208v
4 ? 1,600 vA soft drink machines ? 1 phase 120v
1 ? 1,200 vA copy machine ? 1 phase 120v
1 ? 10 HP Motor ? 3 phase 208v
2 - 5 HP Motors ? 3 phase 208v
1 - Special Appliance 22.6 Amp ? 3 phase 208v
60 ? receptacles @ 180vA each ? 1 phase 120v
5 ? 12 kW feeders ? 1 phase 208v
**********************************************
Amperage Method
Work all of the three phase equipment first.
A B C N
41.63 41.63 41.63 0
41.63 41.63 41.63 0
22.20 22.20 22.20 0
30.8 30.8 30.8 0
16.7 16.7 16.7 0
16.7 16.7 16.7 0
22.6 22.6 22.6 0
192.26 192.26 192.26 0
Add in the single phase line to line loads:
57.69 57.69 0 0
0 57.69 57.69 0
57.69 0 57.69 0
57.69 57.69 0 0
0 57.69 57.69 0
173.07 230.76 173.07 0
Add in the single phase line to neutral 120 volt loads:
13.33 0 0 13.33
0 0 13.33 13.33
13.33 0 0 13.33
0 0 13.33 13.33
10 0 0 10
30 30 30 30
66.66 30 56.66 93.32
TOTALS
431.99A 453.02A 421.99A 93.32A
************************************************
Volt-ampere Method
Work all of the three phase equipment first:
A B C N
5,000 5,000 5,000 0
5,000 5,000 5,000 0
2,666.6 2,666.6 2,666.6 0
3,699 3,699 3.699 0
2,005 2,005 2,005 0
2,005 2,005 2,005 0
2,712 2,712 2,712 0
23,087.6 23,087.6 23,087.6 0
Add in the single phase line to line loads:
6,000 6,000 0 0
0 6,000 6,000 0
6,000 0 6,000 0
6,000 6,000 0 0
0 6,000 6,000 0
18,000 24,000 18,000 0
Add in the single phase line to neutral 120 volt loads:
1,600 0 0 1,600
0 0 1,600 1,600
1,600 0 0 1,600
0 0 1,600 1,600
1,200 0 0 1,200
3,600 3,600 3,600 3,600
8,000 3,600 6,800 4,800
TOTALS
49,087.6 50,687.6 47,887.6 11,200
If you take the single phase line to line load on phase A (23,087.6) and divide by 120 you get 192.3 Amperes. Same Math!! Same for Phase B & C. ?WORK THE MATH?
If you take the line to line single phase load on phase A (18,000) and divide by ? the line to line voltage which is 104v, you will get 173.07 Amperes. Same Math!! Same for Phase B & C. ?WORK THE MATH?
If you take the single phase line to neutral load on phase A (8,000) and divide by 120 you get 66.66 Amperes. Same Math!! Same for Phase B & C. ?WORK THE MATH?
That being said, I believe that you have to break out your loads in the following order and then add together your totals.
First list all three phase loads in category #1, Secondly list all single phase line to line loads in category #2 and Thirdly list all line to neutral 120 volt loads into Category #3.
I welcome your comments. If you care to contact me directly my e-mail address is: