IMHO, calling two phase legs plus the neutral of a 120/208 system 'single phase' is quite a confusing misnomer.
The _only_ sense that it is 'single phase' is that you have two 'hot' legs plus a grounded conductor, and can thus use common single phase service equipment. By this meaning, 'single phase' service equipment with suitable voltage ratings could be used for a corner grounded delta system.
With a polyphase system, power can always be delivered to the load by some combination of the supply phases. This cannot be true in a single phase system; the available power always drops to zero at two points on the supply cycle. With a polyphase system of _any_ phase count, you can use transformers to derive a polyphase system of any other phase count. But with a single phase system you need some form of energy storage to derive a polyphase output, eg. an VSD with its capacitor bank, or a rotary phase converter with its spinning rotor.
Smart $ said:
From the utilization perspective, a 120/208Y system is a single phase supply in the sense only 1? loads can be powered by this portion of the complete system. The same is true if you were to connect a 120/240 subpanel to a 240?/120 service. Only 1? loads can be powered from the subpanel.
I disagree. As you note:
Smart $ said:
The 208V load's curent, 10A, is out of phase by 30? with that of the system voltage applied at each end. This has the effect of a 30? power factor:
A unity power factor load from leg A to neutral will have a different phase angle from a unity power factor load between leg A and leg B. If we call leg A to neutral our reference phase 0?, then leg B to neutral becomes 120?. The inverse of leg A added to the inverse of leg B, derived, for example, using suitable 120V to 120V isolation transformers, would be a derived leg C, at 240?.
I posit that with any three conductors of a three phase system, eg. two phases plus neutral, you can re-derive the entire three phase system with suitable transformers. I believe that 'open-wye to open-delta' transformers are sometimes used for distribution.
hardworkingstiff said:
I wish I was a little more educated. I don't understand why you would calculate power for a 208 load using 120-volts.
Smart$ was giving you the basic principal behind your question. With the 120Y/208 'single phase' system, you have a real phase angle difference between your two supply legs, as referenced to the neutral. Even though your load is unity power factor, the current flowing through it must be in phase with the voltage connected to it. The current is in phase with the 208V. It turns out that the 208V is 30? out of phase with the 120V legs.
hardworkingstiff said:
I think we can agree that if there is a load of 2080 watts at 208 (just from one residence), there would be 10-amps on one leg, 10-amps on the other leg, and 0-amps on the neutral going back to the transformer. If the load was 2400 watts @120-volts split evenly between the 2 legs, then there would be 10-amps on one leg, 10-amps on the other leg, and 10-amps on the neutral. It just seems to me that that 10-amps on the neutral has to go somewhere, it just doesn't dissapear in thin air (or does it?).
Think about the currents flowing into the 'neutral point'. The rule is that the sum of all current flowing into or out of a point must be zero; electrons cannot 'pile up'.
In the 208V situation, you have a circuit of 2 coils and the load. The _voltages_ developed by the two coils are not in phase; that is why two 120V coils in series will only sum to 208V. But the _current_ flowing through the entire circuit _must_ be the same, and thus must be in phase. It happens to be in phase with the _sum_ voltage of the two coils.
In the dual 120V situation, you have _two_ circuits that happen to share the neutral point. The currents in these two circuits are in phase with the individual coil voltages, thus the currents of these two circuits are no longer in phase. Coming into the neutral point, you have three 10A currents, one from each of the coils, and the net current of the two circuits. These three currents happen to phase balance such that the net is zero.
hardworkingstiff said:
Back to the scenario of losing one winding. You would be left with 2 windings connected in series with the center tap being grounded, just like the secondary of a single phase transformer. What's the difference?
The difference is that in the 240V center tapped situation, the two coil voltages are in phase, but in the 'two legs of a wye' situation, the two coil voltages are not in phase.