I finally got it through my head a key point that Jim is making.
A three wire 120/208 service is _defined_ by the documents that he references as a _single phase_ service. It isn't single phase service because there are no phase angle differences; it is a single phase service because that is what it has been named.
Jim has agreed, and I think that we've beaten to death the fact that there are phase angle differences between the two line-common voltages present in such a service.
In general practise, no active use is made of the phase angle differences present in a three wire 120/208 service. As this service is _used_ it is single phase.
To understand the _theory_ behind this service, it must be treated as _two_ legs of a three phase service, and this will show up in things like calculation of neutral current and the like.
We call a three wire 120/208 service a single phase service, even though there are _3_ conductors and thus _3_ different voltage phase angles. It is called this because of the way it is used.
We call a 3 wire 480V delta service a _three phase_ service, and it has _3_ different voltage phase angles.
But we call 4 wire 208Y/120 service a _three phase_ service. This is the name that we give it, even though there are _4_ conductors, _6_ conductor pairs, and thus _6_ different voltage phase angles.
We call a 3 wire 480V corner grounded delta service a _three phase_ service, although it only requires _two_ poles on the breakers, and could be provisioned using a suitable 480V "single phase" panel.
-Jon
A three wire 120/208 service is _defined_ by the documents that he references as a _single phase_ service. It isn't single phase service because there are no phase angle differences; it is a single phase service because that is what it has been named.
Jim has agreed, and I think that we've beaten to death the fact that there are phase angle differences between the two line-common voltages present in such a service.
In general practise, no active use is made of the phase angle differences present in a three wire 120/208 service. As this service is _used_ it is single phase.
To understand the _theory_ behind this service, it must be treated as _two_ legs of a three phase service, and this will show up in things like calculation of neutral current and the like.
We call a three wire 120/208 service a single phase service, even though there are _3_ conductors and thus _3_ different voltage phase angles. It is called this because of the way it is used.
We call a 3 wire 480V delta service a _three phase_ service, and it has _3_ different voltage phase angles.
But we call 4 wire 208Y/120 service a _three phase_ service. This is the name that we give it, even though there are _4_ conductors, _6_ conductor pairs, and thus _6_ different voltage phase angles.
We call a 3 wire 480V corner grounded delta service a _three phase_ service, although it only requires _two_ poles on the breakers, and could be provisioned using a suitable 480V "single phase" panel.
-Jon