hardworkingstiff said:
A 120/240-volt single-phase transformer has the grounded conductor hooked up so there is no influence from any other power source. The 'neutral' is only connected (in the center) of the windings.
A 208Y/120-volt has the neutral connected to the end of three seperate windings. Even though only two (legs, phases, whatever) are brought to a house served with 208/120-volt single phase, doesn't the winding (that was not brought to the house) still influence the voltage at the house?
Let's say legs A and B along with the neutral are brought to your house. The winding for leg C goes out, A and B are still OK. What happens to the voltage in your house? Do you still have 208/120? Something tells me you don't, you have 208/???. Without the C winding, won't you lose some of the 120-volts?
edit: In my simple mind, it seems you would have 208/104 since you then have the neutral tapped in the center of two windings (with no additional influence) just like the single-phase transformer.
If you ignore the primary windings you would have a point. . But obviously you can’t ignore the primary windings. . Whether or not the 3rd phase coil is present, the voltages induced in the secondary coils hit maximum voltage value 120? apart. . 208/104 could only be achieved if they were 180? apart.
Using the simplest example possible, take the residential 120/240 3wire as the example. . Single coil of wire in the transformer secondary. . The grounded point is always the flat line base line that all compares to in the sine wave.
If you ground the center tap wire you get 2 sine wave values of identical voltage levels, but 180? apart. . It’s the result of looking from the center point of the coil in one direction for one value and then in the other direction for the other value.
Now if you ground one end of the coil, you’ll still get 2 sine wave values, but this time one with be double the voltage of the other one and both values with be in phase or 0? apart. . It’s the result of looking from one end of the coil to the center point for one value and then looking farther in the same direction to the farthest opposite end of the coil for the other higher voltage value.
You have to first totally understand what your looking at in the basic 120/240 single coil before you can move on and understand other things. . If you can understand how you can have one coil, one induced voltage, and yet 2 separate sine wave values, then you can move on.
But in your example you would still have 2 separate induced voltages 120? apart because of the primary coils.
hardworkingstiff said:
A 208Y/120-volt has the neutral connected to the end of three seperate windings. Even though only two (legs, phases, whatever) are brought to a house served with 208/120-volt single phase, doesn't the winding (that was not brought to the house) still influence the voltage at the house?
No, the ratio between primary and secondary determines the voltage.
hardworkingstiff said:
Let's say legs A and B along with the neutral are brought to your house. The winding for leg C goes out, A and B are still OK. What happens to the voltage in your house? Do you still have 208/120? Something tells me you don't, you have 208/???. Without the C winding, won't you lose some of the 120-volts?
“winding for leg C goes out, A and B are still OK. What happens to the voltage in your house? Do you still have 208/120?”
Yes, still 208/120. . The amperage levels will be affected, not the voltage levels. . Currents from one coil circulate in the other coils so losing one coil will effect the current in the remaining coils.
David