winnie
Senior Member
- Location
- Springfield, MA, USA
- Occupation
- Electric motor research
mivey said:I'm not sure about the 2-phase 4-wire system. There has to be a common reference point if you are going to tie two separate 2-wire systems together.
I don't believe that this is true.
I believe that in the history of '2 phase' systems, all of the following were used:
2 phases with common end points, requiring 3 conductors (the 'L' shape that you mention)
2 phases with common center taps, requiring 5 conductors (the 'X' that you mention)
2 entirely electrically isolated phases, requiring 4 conductors. The only thing relating the two phases was the fact that they were produced on the same rotating machine, and thus had a definite phase relationship.
mivey said:With two 90-degree displaced coils, you could also have a reference point that was the midpoint of the coils and create a 4-phase system. The 4-phase system was "X" shaped and could have a neutral wire (the 5th wire) coming from the center of the "X". This was the same as joining two 180 degree displaced "L" systems at the corner of the "L".
My understanding is that a system with 4 legs 90 degrees apart is called a 2 phase system, in the same way that 2 legs 180 degrees apart is called a single phase system.
One reference that I've read, describing 'high phase order' motor systems, and dated from the '70s, came up with an interesting naming scheme. Motor coils which were electrically 180 degrees apart 'hemi-phases'...so under this naming scheme a normal 3 phase motor would also be a 6 'hemi phase' motor, and a conventional center tapped system would have 2 hemi-phases. I've never seen this naming convention used anywhere else, so I guess the language didn't catch on.
Each phase of a system has 2 phase angles associated with it. A 3 phase 7 wire system (if such were ever built) would have 6 legs, but would still be a 3 phase system.
The 2 phase angles associated with each phase are _not_ equivalent; imagine synching a generator to the grid and throwing the switch when the phase difference was _exactly_ 180 degrees (Not in answer to Mivey's post; just a general statement out to this discussion).
-Jon