winnie said:
...A waveform and its inverse cannot produce a rotating magnetic field without additional phase shifting components. The zero crossings coincide. A standard center-tapped 'single phase' service will produce a sine voltage and its inverse. By this meaning, a waveform and its inverse provides only a single phase...There are clearly two different phase angles because if there were only one phase angle than the waveform would coincide at _all_ points, not just the zero crossings.
Winnie is correct. I think one of the problems is that some fail to recognize that a waveform is defined by its reference points. For example, Rick may not be saying exactly that, but it could be read to sound that way:
Rick Christopherson said:
...You reversed the polarity of your measuring probe, hence, you created the inverse.
I am not saying they can't be considered 180 degrees out of phase mathematically,...
It is not just a mathematical manipulation, it is that way by definition. Take the corners of a 3-wire delta...please (ba-dump-bump)
. I believe most would be happy to say (using a rough example) that the electron sitting on corner "A" is 120 degrees out of phase with the electron on point "B" (please read Winnie's note on the use of the word phase). Now center tap a coil between "A" and "B" and they want to say these must be in phase.
What has made the difference? The answer is that the reference point changed. The reference point is included in the definition of the waveform. The same definition that allows you to say the points "A" and "B" changed from being 120 degrees out of phase to being in phase is the same one that allows you to use the center tap and say "A" and "B" are 180 degrees out of phase.
So, "in-phase" or "out-of-phase" all depends on your reference point (again, see Winnie's note on the use of the word "phase"). Winnie stated that you had to use a phase shifting component to create three phase out of single phase. This is true. When we only have access to the three points provided by the center-tap, we have lost our original reference to the third leg of the delta (or the original neutral point). These original reference points gave us the phase shift we needed to create rotation with the same "A" and "B" legs that do not produce rotation as a single phase pair.
Without a phase shifting component, our new reference has to be one of the legs, or the center tap. If you choose one of the legs, "A" and "B" are in phase. If you choose the center tap, "A" and "B" are out of phase by 180 degrees.
Now, as Winnie has also stated, the 3-wire 120/208 does not act the same because it can create rotation because it did not lose its original reference which gave the phase shift needed for rotation. It is called a single-phase service by some because only single phase loads are served.
Lately, I think I am liking the term "3-wire network service" because it makes a distinction between the 3-wire 120/240 (two line conductors of a delta, center-tapped, and rotation not readily available), and the 3-wire 120/208 (two line conductors of a wye, with the original neutral point, with rotation readily available).
[edit: Perhaps we can say that a service fed by conductors with linear voltage relationships is called a single phase service. We might could also say that a service that is intended to serve only single-phase loads, and is fed by conductors with non-linear voltage relationships, may also be referred to as a single-phase service.]
[edit: changed "legs" to "line conductors"]