hardworkingstiff said:
So,
'A' coil draws 80-amps and 'B' coil draws 80-amps. If the load is connected at 208-volts you have 16.64 KVA.
'A' coil draws 80-amps and 'B' coil draws 80-amps. If the loads are connected at 120-volts you have 19.2 KVA.
Don't forget the original constraint we were given about 10 kW per coil. The single or three L-N loads would be 1.44 ohms, the three L-L loads would be 4.32 ohms, the single L-L load would be 2.16 ohms.
[edit: nevermind, I think you were responding to #388 & #394]
[edit: Here is an example of what you were talking about using the 10 kW setup. Use a single L-L load.
Vcb=207.846<90, R_load=2.16, I=96.225<90,
W_load=207.846 * 96.225 * cos(90-90) = 20 kW (also 20 kVA)
c_coil kVA=120<120 * 96.225<90 = 11.547 kVA
c_coil kW=120 * 96.225 * cos(120-90) = 10 kW]
[edit: Don't mix kVA delivered with transformer kVA. In your example:
For single L-L:
Vcb=207.846<90, I=80<90
kW_load=207.846 *80 *cos(90-90)=16.63 kW
kVA_load = 207.846<90 * 80<90 = 16628<180 = 16.63 kVA
c_coil kW=120 * 80 * cos(120-90) = 8.313 kW (16.63 kW for both coils)
c_coil kVA=120<120 * 80<90 = 9600<-150 = 9.6 kVA
b_coil kVA=120<-120 * 80<-90 = 9600<150 = 9.6 kVA
Note: transformer size is 19.2 kVA total but only 16.63 kVA delivered to load)
Similarly, for L-N:
Vcn=120<120, Vbn=120<-120, Ic=80<120, Ib=80<-120
kW_load_cn=120 * 80 * cos(120-120)=9.6 kW
c_coil kVA=120<120 * 80<120 = 9600<-120 = 9.6 kVA = load c-n kVA
c_coil kW=120 * 80 * cos(120-120) = 9.6 kW
kW_load_bn=120 * 80 * cos(-120--120)=9.6 kW
b_coil kVA=120<-120 * 80<-120 = 9600<120 = 9.6 kVA = load b-n kVA
b_coil kW=120 * 80 * cos(-120--120) = 9.6 kW
Note: transformer size is 19.2 kVA total and 19.2 kVA delivered to load)
]
[edit: For three L-L:
V_coil=120, I_coil=80, watts_coil = 9600 = watts per load, I_load=46.188 amps
Vcb=207.846<90, Icb=46.188<90
kW_load_cb = 207.846 *46.188 *cos(90-90) = 9.6 kW
kVA_load_cb = 207.846<90 * 46.188<90 = 9600<180 = 9.6 kVA
Vca=207.846<150, Ica=46.188<150
kW_load_ca = 207.846 *46.188 *cos(150-150) = 9.6 kW
kVA_load_ca = 207.846<150 * 46.188<150 = 9600<-60 = 9.6 kVA
Ic = Icb + Ica = 46.188<90 + 46.188<150 = 80<120 and Vcn = 120<120
c_coil kVA = 80<120 * 120<120 = 9600<-120 = 9.6 kVA
c_coil kW = 80 * 120 *cos(120-120) = 9.6 kW
Note: total kVA = total kW = 28.8
]
These examples were for wye banks and resistive loads but the same method would apply for delta and non-resistive loads. We usually simplify this because a lot of times we have balanced loads.