David Castor
- Washington, USA
- Electrical Engineer
Years ago we called this an auto transformer.
It's a two-winding transformer, same as the two-bushing cans, just a different primary voltage. Quite common.
Having a hard time following how can any transformer with only 1 primary winding can have the neutral travel all the way back from the substation on its own system. Meaning it always appeared that if every copper water service that I ran one of my amprobes on had current flow they ultility company is using that to provide the other side of primary that is center tapped to grounded conductor ( neutral ). Know that electricity takes the easiest path but it appears in this situation to take numerous paths when a one bushing transformer is used to supply power to say 10 houses like mine. At least 30 paths when you consider 10 of each: copper water service, steel gas service pipe, & cast iron leaded jointed soil pipe. Everybody knows that a 8' ground rod in the middle of cold winter and to make matters worse there is nothing but concrete & blacktop within 12' of ultility pole the ground resistance would be very high so current flow on copper water service would increase.Not an auto transformer if the primary winding's "neutral" or low side is simply connected to the "neutral" connection of the secondary winding!
The neutral is run all the way back to the substation. i.e. out in the country the poles have three high voltage wires (typically 34.5KV between phases, 19.9 KV phase to neutral) and a neutral conductor that is on very small insulators. Wye feeds. I hardly ever see a two bushing transformer on poles around here for the last 60 years I have been looking at them.
The primary and secondary grounded conductors both tie to the same conductor. Is sort of redundant to run two grounded conductors between two poles (one primary and one secondary) if you are going to tie them together on both ends. If you did that then all you did was create a parallel set for what is effectively still one conductor.Having a hard time following how can any transformer with only 1 primary winding can have the neutral travel all the way back from the substation on its own system. Meaning it always appeared that if every copper water service that I ran one of my amprobes on had current flow they ultility company is using that to provide the other side of primary that is center tapped to grounded conductor ( neutral ). Know that electricity takes the easiest path but it appears in this situation to take numerous paths when a one bushing transformer is used to supply power to say 10 houses like mine. At least 30 paths when you consider 10 of each: copper water service, steel gas service pipe, & cast iron leaded jointed soil pipe. Everybody knows that a 8' ground rod in the middle of cold winter and to make matters worse there is nothing but concrete & blacktop within 12' of ultility pole the ground resistance would be very high so current flow on copper water service would increase.
I only read the Abstract and just glanced at the rest of the document so far. From what I have seen I think writer is barking up the wrong tree to some extent. Current in the earth isn't the problem, it is voltage drop on the grounded conductor that is the problem that causes the "stray voltage".I have posted this before, and everyone thinks this is BS. Except for me.
To me its dangerous because every copper water service and steel gas service that I have measured have current flow on them. Believe its back feeding the cheap lazy utility company of only supplying one high voltage line to primary of their transformers. Sounds like something last tried by Tesla 90 years ago. I have connected over a hundred single phase control & power transformers and had to provide two wires to the primary in order to produce a voltage on the secondary. Yes everybody knows that Ultility companies do not have to follow the NEC and get away with too many short cuts.Single-bushing primary transformers are connected line-to-neutral, so the winding is something like 7200:120/240. Pretty common in many parts of the country. Slightly cheaper than the more common two-bushing transformers.
Earth becomes a parallel path, but is not like we are trying to send all the earth current through one electrode far away and one at the substantion either. We have neutral taps to earth on nearly every structure in the distribution system. Many are single ground rods at poles or other small structures with probably 25 plus ohms each. By the time you factor all them scattered around the system you have a very low resistance to earth, until you start putting current on the neutral, then you get a rise in neutral to earth volts because of basic voltage drop that will vary depending on conditions at any particular point in the system.My understanding is that the neutral wire _does_ go all the way back to the substation, except in the very rare case of 'single wire earth return'.
However it is 'multi-grounded' meaning it is connected to ground electrodes all over the place.
So the soil becomes a parallel path, and if the utility has too much voltage drop on that neutral _wire_ then significant current will flow through the soil.
I don't believe the utility is _simply_ being lazy/cheap for using that MGN as a primary circuit conductor; I think there are some benefits with respect to voltage stability and transients during faults ('effective grounding'). With that said, I _don't_ know the details, and I think I'd prefer delta distribution for single phase loads. Perhaps the MGN should only be used for three phase loads which tend to be better balanced.
-Jon
No, electricity takes all paths available to it. More of it travels the "easiest" (lowest resistance) path than others.Know that electricity takes the easiest path but it appears in this situation to take numerous paths...
?????This is asinine to me. So, the utilities say "So What" we have willing victims that don't know anything about electricity.
An MGN does result in the possibility of stray current traveling through the earth, however negative effects are quite rare. This is one of those things that, as people often do, they overstate the risks and understate the benefits. That is my issue with that Zipse paper: it's not that the stray current issue doesn't exist and is made up, but he drastically overstates the risks and problems and doesn't talk about the benefits.?????
Two wires go from substation to pole pig. What does it matter if we call one wire a phase or a neutral if the voltage feeding the pole pig primary matches? NO WHERE is the return current from the pole pig going through the earth unless the "return" conductor is snapped free, same as if a phase is snapped free!
Think LIGHTNING! California has no lightning compared to the number of strikes we have here in Virginia!I think there are some benefits with respect to voltage stability and transients during faults ('effective grounding').
Almost- Unless the intended return conductor has zero resistance, Kirchhoff's law tells that some, albeit probably quite small, current will flow through the grounding conductor to the dirt; granted that it could be 5-6 orders of magnitude smaller, but it'll still be there.NO WHERE is the return current from the pole pig going through the earth unless the "return" conductor is snapped free, same as if a phase is snapped free!
Similar electrocution today, eight people involved at a public fountain.any other metallic path that heads towards the substation, such as a old water, gas main or CATV coax could be a very good parallel path
I see there is another thread on that incident, but I don't think it's appropriate to post that here when we have no idea whatsoever if that was caused by a utility stray current or an mgn issue. You seem to be implying that.Similar electrocution today, eight people involved at a public fountain.