sfav8r
- San Francisco Bay Area
We are doing an install of some equipment that has one board that is pretty fussy about the ground reference. The equipment is served with 1-1/4 EMT and #4 conductors. The conduit is serving as the ground. As an additional item, we were going to run a ground directly to the circuit board to make sure it has a good ground reference. It seems that since the conductor is not required at all, we could just use a #10 since it's just for the circuit board. However, I could also see an argument that if the conductor is present, it has to be sized for the conductors. Any thoughts and or code references to confirm either way?
Thank you
Thank you