We are doing an install of some equipment that has one board that is pretty fussy about the ground reference. The equipment is served with 1-1/4 EMT and #4 conductors. The conduit is serving as the ground. As an additional item, we were going to run a ground directly to the circuit board to make sure it has a good ground reference. It seems that since the conductor is not required at all, we could just use a #10 since it's just for the circuit board. However, I could also see an argument that if the conductor is present, it has to be sized for the conductors. Any thoughts and or code references to confirm either way?