peter d
Senior Member
- Location
- New England
I agree with Big John. Likewise, I can bury plumbing PVC in the ground then pull UF cable through it. That's a totally compliant installation.
I said essentially all I've had to say and can see we're not getting anywhere. I doubt restating it in different words, different ways is going to sway your opinion. Ultimately, it's an AHJ call and I only care about what an AHJ says about my work. I wish you the best in your endeavors.Where does the code make any such distinction about what the wire is fished in? There is never a guarantee of protection, even if a raceway is used. Neither does the code make a distinction about what constitutes protected, which is why their is no listing requirement for sleeves. Thankfully the code isn't this arbitrary: It's either fished and legally unsecured, or accessible and must be secured.
UF doesn't have the same securing and support requirement as NM. In fact, I don't believe any other cable type has the same requirement as NM.I agree with Big John. Likewise, I can bury plumbing PVC in the ground then pull UF cable through it. That's a totally compliant installation.
UF doesn't have the same securing and support requirement as NM.
Go back and read my other posts carefully...Are you suggesting that cables inside of sleeves need to be secured somehow?
It has the same securing and supporting requirements when run as an above-ground cable assembly. 340.10(4).UF doesn't have the same securing and support requirement as NM. In fact, I don't believe any other cable type has the same requirement as NM.
I think his position is that the requirements for support basically mean it's illegal to sleeve, 334.30(B)(1) notwithstanding.Are you suggesting that cables inside of sleeves need to be secured somehow?
Which sends you to Article 334, Parts II and III... so above ground, installed as nonmetallic-sheathed cable it is no different... so you want to go around the block again. :roll:It has the same securing and supporting requirements when run as an above-ground cable assembly. 340.10(4).
I suggest you actually read each article. To me, it seems each article ranges from just a bit different to almost radically different. So if you want to say that they're all the same, it's because you are only reading what you want to read, and not what is actually there. "Basically the same" is about like saying they are all cables.With the exception of the distances involved the rules for supporting NM are basically the same as every other cable assembly.
So installing a plumbing pipe sleeve for UF in the dirt is perfectly acceptable, but mount that same sleeve on a wall and it becomes a violation?Which sends you to Article 334, Parts II and III... so above ground, installed as nonmetallic-sheathed cable it is no different.... :roll:
All flexible wiring methods allowed to be fished have virtually identical wording about being installed unsecured an unsupported.Smart$ said:So if you want to say that they're all the same, it's because you are only reading what you want to read, and not what is actually there....
FYI- It's Nonmetallic-Sheathed Cable....not the "R" word.....but those who dislike me will relish in that statement:angel:
With the exception of the distances involved the rules for supporting NM are basically the same as every other cable assembly I think his position is that the requirements for support basically mean it's illegal to sleeve, 334.30(B)(1) notwithstanding.
334.15(C) In Unfinished Basements and Crawl Spaces. Where
cable is run at angles with joists in unfinished basements
and crawl spaces, it shall be permissible to secure cables
not smaller than two 6 AWG or three 8 AWG conductors
directly to the lower edges of the joists. Smaller cables
shall be run either through bored holes in joists or on running
boards. Nonmetallic-sheathed cable installed on the
wall of an unfinished basement shall be permitted to be
installed in a listed conduit or tubing or shall be protected
in accordance with 300.4. Conduit or tubing shall be provided
with a suitable insulating bushing or adapter at the
point the cable enters the raceway. The sheath of the
nonmetallic-sheathed cable shall extend through the conduit
or tubing and into the outlet or device box not less than
6 mm (1⁄4 in.). The cable shall be secured within 300 mm
(12 in.) of the point where the cable enters the conduit or
tubing. Metal conduit, tubing, and metal outlet boxes shall
be connected to an equipment grounding conductor complying
with the provisions of 250.86 and 250.148.
In spite of all that is said it is interesting that 334.15 (C) states a listed conduit must be used. One can say that that is only for basements as that is the section quoted but I think you may be able to look ahead a bit at this and come to a conclusion.
I realize it does not say it must be---
True, but it continues to say "or shall be protected in accordance with 300.4."Not only does it not say required, it says shall be permitted.
So I don't see that meaning anything.
It's only "permitted" as an alternative to 300.4. Realistically, what in 300.4 covers [otherwise] surface-run NM?It seems odd that they would say a listed conduit shall be permitted. That seems to indicate that a non listed one is not permitted
True, but it continues to say "or shall be protected in accordance with 300.4."
So what is the alternative?
Also, does this not seem to express that listed conduit or tubing offers some level of protection?
It seems odd that they would say a listed conduit shall be permitted. That seems to indicate that a non listed one is not permitted
Don't shoot the messenger.So installing a plumbing pipe sleeve for UF in the dirt is perfectly acceptable, but mount that same sleeve on a wall and it becomes a violation?
You have to read and interpret each section as a whole... and each respective section is not virtually the same. Looking only at part of a section doesn't always give you the whole picture on compliance.All flexible wiring methods allowed to be fished have virtually identical wording about being installed unsecured an unsupported.
Don't shoot the messenger.
You have to read and interpret each section as a whole... and each respective section is not virtually the same. Looking only at part of a section doesn't always give you the whole picture on compliance.