So where does extra current go with bad distortion PF (Standard VFD input)?

Status
Not open for further replies.

mike_kilroy

Senior Member
Location
United States
A recent thread examined displacement PF and VFDs. It was shown this displacement PF stayed inside and on the output of the VFD so did not effect the AC input to the VFD.

So many say since the input displacement PF to the VFD is nearly 1, there is no extra input current, like out of phase, or 'imaginary.'

Others point out the input RMS current can be 2,3,4,5 times HIGHER that to produce power in the motor at output; yet since displacement PF is effectively 1.0, how can this be? So where does this extra rms current GO? It is caused by distortion PF, even though it is effectively in phase current.

Example: Our 460vac 3 ph input VFD outputs 460Vac 3ph into a fully loaded motor pulling 6 amps RMS in phase current (forget the out of phase aka magnetizing aka imaginary current flowing back and forth from VFD to motor). So assuming near 100% efficiency of the VFD, we expect to see same 6 amps RMS at VFD input terminals. But the input RMS current is measured at 12 amps!

Where does the extra 6 amps go?? Is it real? Imaginary? Power Factor?

Understanding THIS will go a long way to helping eliminate confusion and helping some folks grasp the whole picture.

Where does the extra 6 amps go??
 

Ingenieur

Senior Member
Location
Earth
Sounds implausible

???
motor hp
pf
eff
total motor current
any line filters or reactors
line side pf caps
???

something does not compute
unless the vfd has a bad pf ~0.70
 

mike_kilroy

Senior Member
Location
United States
motor hp - irrelevant
pf- irrelevant
eff- irrelevant
total motor current- irrelevant
any line filters or reactors- irrelevant
line side pf caps- irrelevant
 

topgone

Senior Member
motor hp - irrelevant
pf- irrelevant
eff- irrelevant
total motor current- irrelevant
any line filters or reactors- irrelevant
line side pf caps- irrelevant

Things are "converted" in a vfd. You can't expect the same values at its input and the output.:D
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
170706-2027 EDT

mike_kilroy:

Measure the real power at the motor input or VFD output.

Measure the real power input to the VFD at its input terminals.

Measure the RMS input current to the VFD at one input terminal.

Measure the RMS input voltage to the VFD at its input terminals.

Use a scope to simultaneously measure input current and voltage at the VFD input.

Show us this data.

.
 

Ingenieur

Senior Member
Location
Earth
motor hp - irrelevant
pf- irrelevant
eff- irrelevant
total motor current- irrelevant
any line filters or reactors- irrelevant
line side pf caps- irrelevant

sure is relevant for the conditions stated
you seem to imply the 6 A to the motor is all real power 'forget imaginary current'
or that there is no reactive current

1.732 x 12 x 460 = 9.6 kva in
1.732 x 6 x 460 = 4.8 kw out
vfd pf = 0.50

if there are caps or reactors after the input measurement location it will have an effect
 
Last edited:

Smart $

Esteemed Member
Location
Ohio
...

Where does the extra 6 amps go??
I'm with Ingenieur as to 12A-rms in and 6A-rms out being plausible, at least with a highly-efficient, modern VFD. Perhaps a much older VFD? IDK. Not my forte.

Nevertheless, you cannot violate the physics of the matter.

PowerIN – internal losses = PowerOUT

Break it down from there...

FWIW, what appears as missing power is obscured by the waveforms, output voltage included... and that is where the distortion power factor enters the picture.
 

Ingenieur

Senior Member
Location
Earth
Drive is 100% eff
P in = P out = 4.8 kw
9.6 kva = 4.8 kw + jQ kvar
Q = 8.3 var
S = 9.6 / 60 deg (can't determine lead or lag)
pf = cos 60 = 0.5

something beyond the measurement point is consuming/supplying reactive power
since the motor apparently needs none pf=1
 

Sahib

Senior Member
Location
India
One thing we used to is power, whether it is active or reactive, always flows ie input power=output power. But this not the case with distortion power ie it is not conserved. May be that is the point OP is trying to make!
 

Besoeker

Senior Member
Location
UK
A recent thread examined displacement PF and VFDs. It was shown this displacement PF stayed inside and on the output of the VFD so did not effect the AC input to the VFD.

So many say since the input displacement PF to the VFD is nearly 1, there is no extra input current, like out of phase, or 'imaginary.'

Others point out the input RMS current can be 2,3,4,5 times HIGHER that to produce power in the motor at output; yet since displacement PF is effectively 1.0, how can this be? So where does this extra rms current GO? It is caused by distortion PF, even though it is effectively in phase current.

Example: Our 460vac 3 ph input VFD outputs 460Vac 3ph into a fully loaded motor pulling 6 amps RMS in phase current (forget the out of phase aka magnetizing aka imaginary current flowing back and forth from VFD to motor). So assuming near 100% efficiency of the VFD, we expect to see same 6 amps RMS at VFD input terminals. But the input RMS current is measured at 12 amps!

Where does the extra 6 amps go?? Is it real? Imaginary? Power Factor?

Understanding THIS will go a long way to helping eliminate confusion and helping some folks grasp the whole picture.

Where does the extra 6 amps go??
It doesn't go any where.
 