A recent thread examined displacement PF and VFDs. It was shown this displacement PF stayed inside and on the output of the VFD so did not effect the AC input to the VFD.
So many say since the input displacement PF to the VFD is nearly 1, there is no extra input current, like out of phase, or 'imaginary.'
Others point out the input RMS current can be 2,3,4,5 times HIGHER that to produce power in the motor at output; yet since displacement PF is effectively 1.0, how can this be? So where does this extra rms current GO? It is caused by distortion PF, even though it is effectively in phase current.
Example: Our 460vac 3 ph input VFD outputs 460Vac 3ph into a fully loaded motor pulling 6 amps RMS in phase current (forget the out of phase aka magnetizing aka imaginary current flowing back and forth from VFD to motor). So assuming near 100% efficiency of the VFD, we expect to see same 6 amps RMS at VFD input terminals. But the input RMS current is measured at 12 amps!
Where does the extra 6 amps go?? Is it real? Imaginary? Power Factor?
Understanding THIS will go a long way to helping eliminate confusion and helping some folks grasp the whole picture.
Where does the extra 6 amps go??
I think you stated this wrong. The input to the VFD basically has a 1.0 PF, so it might be 6 amps. However the current to the motor will have a lower power factor (maybe 0.8), so the current to the motor will actually be higher (probably not 12 amps, but maybe 8 amps.)
So I think you are actually asking "Where did the extra 2 amps come from?".
The answer is that reactive power (and current) is not dissipated in heat like real power is. It constantly flows back and forth between the source (the VFD) and the load (the motor).
So when the motor is started or stopped, there may be a transient current surge on the VFD input to get the reactive current flowing (or stopped), but in a steady state condition, the output reactive current doesn't need an equal current on the input to keep it going.