OK, you have a good point that I missed. The metallic service conduit contains a conductor that may be carrying a lightning induced pulse to earth.This is where we differ - especially since we are under the same POCO (PG&E) who rarely installs an electrode at any pole mounted transformer location. (If it weren't raining right now - I would say go outside and take a look.) They are often fully dependant on local grounding at each service for overhead installations via the grounded service conductor. (A means of grounding that is dependant on the service itself being grounded - along with the many others on the system.) The idea the SE conductors would not be involved during a lighting event, even outside of that particular arrangement described, ignores the fact the all available paths would be taken by the current involved in a lightning strike.
So here's a question, if you have a metallic service riser, is it bonded to the neutral at both ends, or just at the meter base? [I honestly don't know, we have an underground service and I've not done any service work.] If the service riser is bonded at only one end, it will be a "choke" for its entire length. In that case, the small amount of service conduit between the meter base and the separate main disconnect would be of secondary importance.
Cheers, Wayne