Stranded wires under screws

Status
Not open for further replies.

Sharpie

Senior Member
Location
PA
Do any of you terminate stranded wires under screw terminals (i.e. Recepts, or ground screws)?

Another question: What about solid wires under "pressure plate" style terminals?

Just curious about opinions.
 

220/221

Senior Member
Location
AZ
Stranded wire under a screw only in a pinch with no fork terminals available.

"pressure plate" style terminals will take any wire nicely.
 

iwire

Moderator
Staff member
Location
Massachusetts
IMO the only thing a fork terminal accomplishes is a better looking installation, I do not believe for a moment that it actually provides a better connection.
 

wireguru

Senior Member
I don't either, but it it less of a pain than wrapping stranded around terminals. That's why I prefer the backwired receptacles. :cool:


yep. My question is not 'how do you get a stranded wire to stay under a screw', but why are you using a device that requires you to get a stranded wire to stay under a screw?
 

mikeames

Senior Member
Location
Gaithersburg MD
Occupation
Teacher - Master Electrician - 2017 NEC
Twisting the strands counter-clockwise works fairly well for keeping all the strands under the screw.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
I will leave a tiny piece of insulation on the end of the standed wire when I wrap the wire around a screw terminal. The small piece of insulation will hold the strands together pretty good.

Chris
 

raider1

Senior Member
Staff member
Location
Logan, Utah
I dont know too much but i think the Pass and Seymour CR series receptacles only accept solid.

Yes, according to P&S the CR series devices only accept #14 through #10 solid conductors, while the BR series will accept either stranded or solid wire.

HERE is a link to a page with information on the P&S CR series receptacles.

Chris
 

iwire

Moderator
Staff member
Location
Massachusetts
Intgresting, here is what the white book says.

RECEPTACLES FOR PLUGS AND
ATTACHMENT PLUGS (RTRT)
GENERAL
This category covers general use receptacles for use in wiring systems
recognized by ANSI/NFPA 70, ??National Electrical Code?? (NEC), and
outlets for use in appliances and fixtures. It also covers some attachment
plugs, male inlets, and cord connectors with nonstandard slot or blade
configurations which are part of a line of wiring devices including receptacles.
Other similar attachment plug devices are covered under Attachment
Plugs (AXGV).


snip..

Terminals of the wire-binding screw, setscrew, or screw-actuated back wired clamping types are suitable for use with both solid and stranded
building wires.
 