Re: Switched Din. Rm. Outlet?
stop that im geting dizzy.just go back to racing the cars
stop that im geting dizzy.just go back to racing the cars
[But, that can not be the lighting outlet as required by 210.70(A)(1)/QUOTE]
Where does it say it cant ?
Nothing in nec say we can not plug a lamp into a SA receptacle.I know its hard to swallow but take it one step at a time and have met the requirements for lighting.No it was not what they had in mind ,but we can use nec to sometimes allow bad things.I remember back when taking Mike Holts course about a 14-2 nm being fused at 30 amps legally.
JW, what you've written isn't what 210.70(A)(1)Ex.1 says.I am required to install a lighting outlet as outlined in 210.70. This outlet has to be a lighting outlet. If I decide to use a switched small appliance receptacle then I just made this receptacle a lighting outlet
It actually confirms the opposite of the point you're making.In other than kitchens an bathrooms, one or more receptacles controlled by a wall switch shall be permitted in lieu of lighting outlets.