Am currently designing a separately derived system for the interior of a building, 480/208Y transformer feeding a lighting panel located greater than 75 ft. away, thus requiring secondary conductor protection (breaker in this case) near the transformer per 240.4(F) in conjunction with 240.21(C). Conduit system is EMT. Grounding electrode conductor connection to neutral is in transformer, thus requiring the system bonding jumper connection at the same point. My question is: if I run what I would consider to be the system bonding jumper from the panel ground bus back thru the secondary breaker to the transformer neutral, am I allowed to terminate in the breaker and then continue on with another piece of wire to the transformer neutral? Would this violate the 250.30(A)(1) statement "An unspliced system bonding jumper ...."? Or, can the conductor from the panel ground bus to the breaker ground connection be considered part of the equipment grounding conductor system, in which case the conductor from the breaker ground connection to the transformer neutral could be considered to be the "unspliced system bonding jumper"? Appreciate any help.