I had thought of that. 240.4 is for protection of conductors, not flexible cables and cords. That is covered under 240.5 (I think.) So my example would meet all of the requirements of 240.21.
While it is true the overcurrent provisions for cords and cables fall under 240.5, but as you follow those requirements they always refer back to the branch-circuit overcurrent device (in that the CMP assumes they are being fed by a branch circuit rather than a feeder or a secondary tap circuit), even when considered protected by a supplemental overcurrent device.
That was also my interpretation also, until Charlie first raised the point that 240.21(C) didn't explicitly require OCP. Then I came to believe that if the intent of the code was to require OCP on secondaries (except under 240.21(C)(1)) then it WOULD NOT have included the language about terminating on a DEVICE.
Possibly, but as an OCPD is a device, maybe not.
240.21(C)(2)(1)(b) refers to device and overcurrent protective device separately in the same sentence, so that condition does infer the device is something other than an OCPD.
However, as I said before, compliance under 240.21 other than the general statement is as specified in (A) through (H), and under 240.21(C) compliance is required with 240.21(C)(1) through (C)(6). It does not say one of (C)(1) through (C)(6), so an installation must comply with all of six. As such, unless precluded from requirements therein by text within each of the six conditions, it must comply with any that are applicable.
The above means that when secondary tap conductors are protected by the primary OCPD under 240.21(C)(1), they must also comply with 240.21(C)(2) because it is not render inapplicable by the text therein. (C)(3) through (C)(6) all require the secondary tap conductors to terminate at a single OCPD, so they are inapplicable.
Also note (C)(1) is about protection only, whereas (2) through (6) are about distance right up front in the title, and only then goes on about any required protection... but in the case of 240.21(C)(2)(1)(b) it is an "or" statement with "device" and "overcurrent protective" as the subjects. So as I said before, it is stated this way only to permit a 240.21(C)(1) installation of a device rather than an OCPD at the secondary tap conductors termination.
Note the preceding is a literal interpretation of the Code, and not one of intent.