wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
Well, I'm just applying Charlie's rule without any preconceptions.I'm done. Good luck with your interpretation. :happyyes:
Cheers, Wayne
Well, I'm just applying Charlie's rule without any preconceptions.I'm done. Good luck with your interpretation. :happyyes:
That's fine... but there are some instances where that gets you in trouble... and this is one of them. Some industry-accepted principles are not written as codified text simply because they are, well, industry accepted... :slaphead:Well, I'm just applying Charlie's rule without any preconceptions.
Cheers, Wayne
As I said to Don, if a conductor is a feeder and a branch circuit conductor, then it has to comply with rules for both. Since they are different roles, they have different rules. If someone could actually point out a conflict between the rules for the two uses, I'd be more than happy to concede that the NEC prohibits that situation. But absent any such conflict, it is NEC compliant.If circuit conductors are permitted to be both feeder and branch circuit conductors, why bother with the separate definitions and articles to begin with.... just sum 'em all up in an article titled "Circuits".
Wow I had no idea this post would generate so much discussion. One of the responses on page 1 asked what size conductors I would use between the tap point and the 20A fuses -- my initial thought was that these would be #12, but it seems like some posters believe these conductors should be rated for 60A.
Maybe I should ask my question a different way: If you believe the circuit description in my original post to be a violation, how would you change things such that the installation is code compliant?
Thanks again for the feedback.
Wow I had no idea this post would generate so much discussion. One of the responses on page 1 asked what size conductors I would use between the tap point and the 20A fuses -- my initial thought was that these would be #12, but it seems like some posters believe these conductors should be rated for 60A.
Maybe I should ask my question a different way: If you believe the circuit description in my original post to be a violation, how would you change things such that the installation is code compliant?
Thanks again for the feedback.
If you add conductors to an OCPD to a load, those new conductors are certainly a feeder, because of the downstream OCPD. So regardless of what you call the original conductors, you can apply the feeder tap rules to them. The 'feeder' in 'feeder tap' refers to what you are making, not where you get the power.But was I reading correctly that Wayne was proposing that the act of tapping it, turns it into a feeder and now we can use the feeder tap rules?