Here again we have a misconception of what constitutes the service.
If I set a 200 amp panel with a 200 amp main breaker that has space for 42 circuits, what part of this enclosure is the service?
Answer; There will be a possible of four points in this enclosure that will constitute the service. They are as follows;
1) Where the ungrounded (hot) conductors land and the 200 amp breaker (main disconnecting means)
2) The point where the grounded (neutral) conductor lands,
3) The main bonding jumper,
4) The grounding electrode conductor should it be installed in the enclosure as outlined in 250.24(A)(1)
Any thing else that is contained in this panel will need to conform to 408. The service ends with the disconnecting means.
408.3(A)(2) mandates that no uninsulated, ungrounded service busbar or service terminal is exposed to inadvertent contact by persons or maintenance equipment while servicing load terminations.
The only way that this can be achieved is by having a disconnect that will turn everything in the panel off such as a main disconnect.
408.34 define the difference between a power panel and a lighting and appliance panel. The big question is how is the enclosure that is being used for the temp power listed. Is it a panel? Then 408 will apply.