Re: Temporary Service
Rick,
408.36 applies no matter where the panel is used. The panel must have overcurrent protection on its supply side. That can't be done for a service panel unless you have an main breaker.
Don
Rick,
408.36 applies no matter where the panel is used. The panel must have overcurrent protection on its supply side. That can't be done for a service panel unless you have an main breaker.