Originally posted by iwire:
Pierre I am not following you.
If I understand you correctly you are saying that any of the services I see on a regular basis that consist of a large panel (1000 to 3000 amps) board with 6 breakers all 800 amps or less are illegal.![]()
Hi Mike, for now forget about the distentions between panel boards. (Which I am well aware of)Originally posted by jwelectric:
Bob,
Could what you are referring to in this post be a switch gear (power panel board)?
Again forgetting about the need for a main in L&A panels for a moment I am confused why Pierre would say these breakers do not disconnect that premises from the service conductors.Originally posted by pierre:
The reason I said the 408.36 is not applicable here is because of 230.70. We need to disconnect all conductors in the building from the service conductors.
Two GFCI circuit breakers are not disconnecting the service conductors, if the service conductors are terminated to a MLO panel.
David I just can not agree with that, it is not protection it is just design no more.Originally posted by david:
Now the only protection for the service conductors comes in the form of design and the code does require over load protection in that form
Article 450 has nothing to do with the required protection of conductors, panels or any equipment other than transformers. The issue in this thread is not the protection of a transformer.Don,With regards to secondary xfrmr protection, look at note 2 table 450.3(B).IT allows the 6-hand rule.
That exception does not permit that. As I stated before, that exception only applies when the panel is served by a feeder, it does not apply when the panel is served by service conductors. The exception requires line side overcurrent protection for the panel. You cannot provide overcurret protection at the load end of the supply conductors. You can only provide overload protection at the load end of the conductors. There is no code compliant way to install a lighting and appliance branch circuit panel unless you provide overcurrent protection on the supply side of the panel. There are only two ways that this can be done. One, the panel is supplied by a feeder that has an overcurrent device with a rating equal to or less than that of the panel, or two, use a main breaker in the panel. Again, there is nothing in Article 230 that modifies the requirement that a lighting and appliance branch circuit panel have overcurrent protection on its supply side. Just because it has always been done that way or just because everyone does it that way does not make it code compliant.The provisions of 408.36 excep.#1 allow the use of not having individual protection when the ampacities of all the brkrs. are not greater than the rating of the panel.
What? I don't understand that statement. What secondary conductors are service conductors?My point is that secondary conductors are actually service conductors and fall under 230.71.and when using a panel board as service equip.
Can you explain what is ment by "Separately Derived System"?Originally posted by RUWired:
If i included it (feeder) or not, the same exception still holds.The NEC has always allowed the 6-hand rule, and all i am saying is that this article backs it up.These 6 overcurrent devices are protecting the feeder(the service in this case). The same can be true in xrfmr secondary conductors.
Rick
David I have never seen that, I have seen 230.90(A) Exception 3 that simply requires the service conductors to exceed the calculated load.Originally posted by david:
Bob.
Somewhere the Code says the service is sized to the actual or calculated load whichever is greater can't find it right now though
connected to calculated