The problem with this section is the word "near". The definition of near can mean many things to many people. I would think that as long as a person is wearing the appropriate PPE and does not cross the prohibited approach boundary as defined by NFPA70E then the work is allowed. This of course assumes that arc flash hazards are known and adequate arc flash PPE is a available. Just my opinion.
2012 70E provided some clarification
130.2 Electrically Safe Working Conditions.. Energized electrical conductors and circuit parts to which an employee might be exposed shall be put into an electrically safe work condition if any of the following conditions exist:
(1) The employee is within the Limited Approach Boundary.
(2) The employee is within the Arc Flash Boundary.
(3) The employee interacts with equipment where conductors or circuit parts are not exposed, but an increased risk of arc flash hazard exists.
and...
(B) Energized Electrical Work Permit.
(1) When Required. When working within the limited approach boundary or the arc flash boundary of exposed energized electrical conductors or circuit parts that are not
placed in an electrically safe work condition (i.e., for the reasons of increased or additional hazards or infeasibility per 130.1), work to be performed shall be considered energized electrical work and shall be performed by written permit only.